Bad 2200XL or Replace Batteries?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Bad 2200XL or Replace Batteries?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Kenneth_apc
Crewman Kenneth_apc
Crewman

Posted: ‎2021-07-07 10:30 PM . Last Modified: ‎2024-03-04 10:30 PM

0 Likes
7
3286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:30 PM . Last Modified: ‎2024-03-04 10:30 PM

Bad 2200XL or Replace Batteries?

I picked up used Smart-UPS 2200XLNET on the cheap thinking that I might need to replace the batteries. When I turn it on it beeps after a few seconds and lights up the replace battery indicator. Will replacing the batteries positively fix the problem or is it possible there could be something else wrong with the unit. I don't want to spend the money getting new batteries if that won't fix the unit.

Thanks,

Ken

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 2200
  • battery
  • error
  • power
  • replace
  • smart-ups
  • smartups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-07 10:30 PM . Last Modified: ‎2024-03-04 10:30 PM

0 Likes
0
3286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:30 PM . Last Modified: ‎2024-03-04 10:30 PM

If you ordered a genuine APC RBC pack, it should be plug-and-go. If you ordered generic batteries, before you remove the cables from the old batteries, take pictures of where all the cables go and how the batteries are laid out, and duplicate that when attaching the cables to the replacement batteries. There are consequences to doing it wrong, ranging from not being able to fit the batteries back into the UPS, to the UPS not detecting the batteries, to ka-bloom (another poster here had that happen when they hooked the batteries up backwards). Also, don't wiggle the F2 connectors on the battery cables too much when removing them, or you can end up with poor connections which cause problems. If they are loose on the new battery terminals, you can carefully squeeze the curled-over part of the connector to tighten its grip. Of course, this is not supported or recommended by APC - that's one of the reasons they sell complete RBCs. One last hint is that sometimes the batteries that make up a set are stuck together with double-sided sticky foam tape. That helps you not need an extra set of hands when trying to slide the whole mess back into the UPS. Your local office megastore should have this if you want to stick the new batteries together.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:30 PM . Last Modified: ‎2024-03-04 10:30 PM

0 Likes
0
3286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:30 PM . Last Modified: ‎2024-03-04 10:30 PM

On the replace battery indicator, is it solid or flashing? I'd probably measure the voltage on the batteries in thUPS and look for a date code on the batteries to see if you can tell how old they are just to get an idea.

Some of these older UPSs, if they have been turned off/discharged for a very long time will require good batteries to start up. It does sound like batteries will solve the issue but it is really tough to be 100% positive. That is why I suggest to measure the voltage on the batteries and see if you can find out how old they are to help make the decision a little easier. If these did seem to be "new" batteries then I'd be a little more skeptical.

If you were to try batteries, I'd validate the return policy on whereever you get them just in case there is a problem with the UPS that you won't be able to know before you get good batteries in there and try to start it up and find there to be another hardware fault or something.

Reply

Link copied. Please paste this link to share this article on your social media post.

Kenneth_apc
Crewman Kenneth_apc
Crewman

Posted: ‎2021-07-07 10:30 PM . Last Modified: ‎2024-03-04 10:30 PM

0 Likes
0
3286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:30 PM . Last Modified: ‎2024-03-04 10:30 PM

The replace battery indicator is solid red with a constant chirping. The date code wasn't punched on any of the batteries so I can't tell how old they are. The voltages I measured across the four batteries were 4.8v, 4.7v, 4.5v and 3.1v. The last battery was split open along one edge so that one is bad. It doesn't look like it leaked and there was no corrosion in the UPS case.

They looked like replacement batteries because the label said Universal Battery. The battery model was UB12180 and it was rated at 12v and 18Ah. According to the website, my model of APC UPS is a compatible product.

The model of the UPS is SU2200XLNET and the serial number is WS0052005295.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:30 PM . Last Modified: ‎2024-03-04 10:30 PM

0 Likes
0
3286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:30 PM . Last Modified: ‎2024-03-04 10:30 PM

OK, so those should be 12V batteries. I believe in this UPS has them wired in series to create a 48VDC battery system (which floats at 55VDC).

I recommend you look into replacing the batteries and it is a logical next step based on the information you've shared so far. We won't know if there are other problems until the UPS starts up but I do think the discharged batteries are stopping the UPS from starting up.

Reply

Link copied. Please paste this link to share this article on your social media post.

Kenneth_apc
Crewman Kenneth_apc
Crewman

Posted: ‎2021-07-07 10:30 PM . Last Modified: ‎2024-03-04 10:30 PM

0 Likes
0
3286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:30 PM . Last Modified: ‎2024-03-04 10:30 PM

I have ordered new batteries. They should be arriving today. Is there anything special I need to do when replacing them? I have seen a few message threads where some people have had problems when doing this.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:30 PM . Last Modified: ‎2024-03-04 10:30 PM

0 Likes
0
3286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:30 PM . Last Modified: ‎2024-03-04 10:30 PM

What type of problems? To replace batteries on a Smart-UPS, you can do it "hot." You'll just remove any bezel or plate in the way, disconnect the old batteries, (the UPS will technically no have battery back up for this short period of time), you'll see a flashing replace battery LED to indicate there are no batteries, you connect the new ones, let them charge up for at least a few hours in the UPS while the UPS is connected to AC power and turned off (which they should charge like that), then give it a whirl and turn them on. 

The only issues I've seen would be if the old batteries are stuck and had swollen/vented but that is the minority of cases.

Reply

Link copied. Please paste this link to share this article on your social media post.

Kenneth_apc
Crewman Kenneth_apc
Crewman

Posted: ‎2021-07-07 10:30 PM . Last Modified: ‎2024-03-04 10:30 PM

0 Likes
0
3286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:30 PM . Last Modified: ‎2024-03-04 10:30 PM

I've heard of the run time on battery power not being as long as before the battery replacement or run time dropping fairly quickly. I thought there might be some type of configuration that may need to be done.

Since I just acquired the UPS and have nothing connected to it, I figured I would just install the new batteries and plug it in overnight before I try connecting anything to it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-07 10:30 PM . Last Modified: ‎2024-03-04 10:30 PM

0 Likes
0
3287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:30 PM . Last Modified: ‎2024-03-04 10:30 PM

If you ordered a genuine APC RBC pack, it should be plug-and-go. If you ordered generic batteries, before you remove the cables from the old batteries, take pictures of where all the cables go and how the batteries are laid out, and duplicate that when attaching the cables to the replacement batteries. There are consequences to doing it wrong, ranging from not being able to fit the batteries back into the UPS, to the UPS not detecting the batteries, to ka-bloom (another poster here had that happen when they hooked the batteries up backwards). Also, don't wiggle the F2 connectors on the battery cables too much when removing them, or you can end up with poor connections which cause problems. If they are loose on the new battery terminals, you can carefully squeeze the curled-over part of the connector to tighten its grip. Of course, this is not supported or recommended by APC - that's one of the reasons they sell complete RBCs. One last hint is that sometimes the batteries that make up a set are stuck together with double-sided sticky foam tape. That helps you not need an extra set of hands when trying to slide the whole mess back into the UPS. Your local office megastore should have this if you want to stick the new batteries together.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore