Backup UPS 1050 battery discharging overnight while not in use.
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2024-12-1401:57 AM
Backup UPS 1050 battery discharging overnight while not in use.
Can someone explain. My new UPS 1050 was charged up - 4 lights on after about 8 hours as recommended. I left it unplugged overnight and it was flat next morning.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2024-12-1603:00 AM
Hi Tony,
Please upload the data, event, and UPS logs from the APC Power Chute software here.
Remove AC Mains from the wall. Than use a multimeter to measure the battery while disconnected and outside of the unit.
What is the battery voltage?
Connect the battery cartridge back into the system and reconnect the AC Mains.
What is the battery voltage when connected to the main system?!?
Since this is a new system I would encourage you to contact APC Technical Support. Have ready the serial number, purchase receipt, and description of the problem. If the problem is not solved in the APC Forum at least a warranty submission has been started.