BX1500M will not charge batteries unless system is upside down.
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-2902:41 AM. Last Modified: 2024-07-2902:42 AM
If this unit is still under warranty I would encourage you to contact APC Technical Support to initiate a RMA.
The problem you see is an extremely common problem! 🤦♂️👎
The internal contacts for the battery terminals are either bent, broken, or misaligned inside. There are several YouTube videos depicting how to identify and repair the problem if this is within your capability.
Let me know how everything turns out with APC Technical Support. 👍