Trying to reset admin account on AP9617, but terminal session is freezing.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Trying to reset admin account on AP9617, but terminal session is freezing.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
jwaldeck
jwaldeck
Cadet

Posted: ‎2024-07-28 12:50 PM

0 Likes
2
844
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-28 12:50 PM

Trying to reset admin account on AP9617, but terminal session is freezing.

Hi everyone, 

 

I have a AP9617 I bought second hand off of eBay. I'm trying to do a factory reset on it, so I can log into it and enable the web interface. I have no computers with a serial port any longer, so I purchased an APC USB to serial cable off Amazon (https://www.amazon.com/gp/product/B082R3X84J/ref=ppx_yo_dt_b_search_asin_title?ie=UTF8&psc=1). I've got it connected to my UPS, a SUA1500RM2U, and to my laptop. I'm using Putty to connect to it, 2400-8-1-None. I've done flow control none, and XON/XOFF, same result for both. I'm able to log into the interface using apc/apc. But I can't complete the admin reset because the interface freezes. It freezes at different points, it more seems to be a timing issue. I also tried speed 9600, but with that I only get strange characters on the screen, I never get the login interface. Any ideas?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Kirk Teken
Kirk

Posted: ‎2024-07-29 02:34 AM

0 Likes
1
828
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-29 02:34 AM

You’ll want to format the NMC instead of resetting it. Press and hold the reset button on the NMC for 20+ seconds, than release.

 

Once the NMC has been formatted the user name and password is all lower case: apc

 

The NMC should be in DHCP mode so check your router to see what DHCP Leased IP Address is and login. Once logged in you will have a 50/50 chance the NMC firmware installed is for your Smart-UPS.

 

If so you’ll see all the options to manage the UPS. 👍 If all you see is the main page and nothing else or things that don’t apply to your specific unit. 

You will need to change the firmware to reflect the UPS in use. Let me know if you have more questions and good luck! 👍

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Teken
Kirk Teken
Kirk

Posted: ‎2024-07-29 02:34 AM

0 Likes
1
829
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-29 02:34 AM

You’ll want to format the NMC instead of resetting it. Press and hold the reset button on the NMC for 20+ seconds, than release.

 

Once the NMC has been formatted the user name and password is all lower case: apc

 

The NMC should be in DHCP mode so check your router to see what DHCP Leased IP Address is and login. Once logged in you will have a 50/50 chance the NMC firmware installed is for your Smart-UPS.

 

If so you’ll see all the options to manage the UPS. 👍 If all you see is the main page and nothing else or things that don’t apply to your specific unit. 

You will need to change the firmware to reflect the UPS in use. Let me know if you have more questions and good luck! 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

jwaldeck
jwaldeck
Cadet

Posted: ‎2024-07-29 08:22 PM

In response to Teken
0 Likes
0
779
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-29 08:22 PM

Thank you for the reply, I ended up getting the password reset by memorizing the sequence I needed and typing it in before it froze up on me. But this is great info for anyone else in need!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore