Is there any reason I should not use the Back-UPS model with a server. The wattage is at about 50% of the amount rated for this model.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:17 PM . Last Modified: 2024-03-14 02:59 AM
Good day Matt, thank you for contacting the APC Discussion Forums.
There are many reason why we do not recommend using a server on a Back-UPS and I'll list everything that I knew. For the others please feel free to share your inputs.
* Power Factor Corrected Power Supplies - A PFC power supply utitlizes/uses all the power that is being fed into it, in other words whatever that comes in goes out making it a highly efficient device. Please take a look at this [APC Knowledge Base|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=8883&p_created=1193079387&p...]
* Using an APC Smart-UPS, customers would have more choice when it comes to monitoring the UPS and configuring graceful shutdowns on their PCs.
* Step Approximated Sine Wave - For some servers the kind/type of sine wave is important, although the Back-UPS produces a pure sinewave while it is online once it transfer to battery it provide a step approximated sine wave in which some servers does not like. Smart-UPS provides a better voltage conditioning and pure sinewave whether online or on battery.
* Transfer Time - This is the amoount of time that a UPS needs to switch from one state to the other, Back-UPS takes about 4-8 milliseconds while for Smart-UPS depending on the model offers from 2-4 to 0 milliseconds of transfer time. Although this are just very quick transfer times, it can cause the load to reboot.
JonPro
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:17 PM . Last Modified: 2024-03-14 02:59 AM
Good day Matt, thank you for contacting the APC Discussion Forums.
There are many reason why we do not recommend using a server on a Back-UPS and I'll list everything that I knew. For the others please feel free to share your inputs.
* Power Factor Corrected Power Supplies - A PFC power supply utitlizes/uses all the power that is being fed into it, in other words whatever that comes in goes out making it a highly efficient device. Please take a look at this [APC Knowledge Base|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=8883&p_created=1193079387&p...]
* Using an APC Smart-UPS, customers would have more choice when it comes to monitoring the UPS and configuring graceful shutdowns on their PCs.
* Step Approximated Sine Wave - For some servers the kind/type of sine wave is important, although the Back-UPS produces a pure sinewave while it is online once it transfer to battery it provide a step approximated sine wave in which some servers does not like. Smart-UPS provides a better voltage conditioning and pure sinewave whether online or on battery.
* Transfer Time - This is the amoount of time that a UPS needs to switch from one state to the other, Back-UPS takes about 4-8 milliseconds while for Smart-UPS depending on the model offers from 2-4 to 0 milliseconds of transfer time. Although this are just very quick transfer times, it can cause the load to reboot.
JonPro