Assistance For Smart UPS SUA1000XL problem

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Assistance For Smart UPS SUA1000XL problem
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:31 AM . Last Modified: ‎2024-03-17 11:15 PM

0 Likes
2
992
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:31 AM . Last Modified: ‎2024-03-17 11:15 PM

Assistance For Smart UPS SUA1000XL problem

My UPS creating problem with charging and load i have installed two batteries. I using its after three month of shutdown.  I am using it from Last two years.

Some time battery charging indicators blink some time remains static.

Its making too much clicking sound. Its also make clicking sound even it totally poweroff. Red wire connected with positive terminal and black wire to negative terminal, while both batteries -/+ connected to each other. 

Please help guys.

Junaid

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 09:31 AM . Last Modified: ‎2024-03-17 11:15 PM

0 Likes
0
992
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:31 AM . Last Modified: ‎2024-03-17 11:15 PM

On 1/4/2019 10:40 AM, William said:

Note: if the batteries in the UPS have gotten bad enough, it may not be possible to perform a successful calibration. At one time, APC provided a calibration key to solve this problem. I'm unsure if they still do.

My understanding is that calibration using your manual procedure should always work. On some of the older UPSes, issuing a software calibration command would be ineffective because the estimated runtime is too low.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:31 AM . Last Modified: ‎2024-03-17 11:15 PM

0 Likes
0
992
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:31 AM . Last Modified: ‎2024-03-17 11:15 PM

Your Smart UPS is likely in need of a runtime calibration if you have installed new batteries. The blinking battery charge level LEDs indicate that the UPS believes it can only power the load for a short period of time. (By default this is two minutes, but it can be adjusted through UPS management software. You may want to check that value.)

To perform a runtime calibration, you'll need an outlet strip with a switch, properly grounded electrical outlet, and an electrical load of some kind that runs to at least 30% of the UPS's rated capacity. Purely resistive loads (not computers or motors) are best for this, and incandescent light bulbs work well.

1. Safely power down the load to which the UPS is attached. Since the UPS will be away from the load for a while, you may want to put another UPS in place if the load is critically important.

2. Place the UPS in a location where you can work with it easily. Plug the outlet strip into the wall outlet, and the UPS into the outlet strip.

4. Turn the UPS on and let it charge the battery for at least eight hours.

5. Connect your lamps or other dummy loads, turn them on and give them a few minutes to stabilize. It's important that the load remain nearly constant while the UPS is being calibrated.

6. Switch the outlet strip OFF. The UPS should begin carrying the load. Allow the UPS to do so until it shuts down.

7. Allow the UPS to recharge its battery for a minimum of eight hours. Place it back in its original location and reconnect the equipment that needs to be protected.

Note: if the batteries in the UPS have gotten bad enough, it may not be possible to perform a successful calibration. At one time, APC provided a calibration key to solve this problem. I'm unsure if they still do.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 09:31 AM . Last Modified: ‎2024-03-17 11:15 PM

0 Likes
0
993
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:31 AM . Last Modified: ‎2024-03-17 11:15 PM

On 1/4/2019 10:40 AM, William said:

Note: if the batteries in the UPS have gotten bad enough, it may not be possible to perform a successful calibration. At one time, APC provided a calibration key to solve this problem. I'm unsure if they still do.

My understanding is that calibration using your manual procedure should always work. On some of the older UPSes, issuing a software calibration command would be ineffective because the estimated runtime is too low.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore