Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-29 07:10 AM . Last Modified: 2024-03-12 04:41 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:10 AM . Last Modified: 2024-03-12 04:41 AM
after a power cut
power went back and one of my two ups(SMART_UPS 3000 RM) I get a loop with this message
An inverter DC imbalance exists
followed by
The output power is turned off
Please help I have no physical access for the moment
What can I do to make it transmit power to my servers connected to this ups, I do not have other plugs to connect them.Any possibility to make it by pass?
Any ideas welcome, I will have onsite access within 24 hours but I would like to know what to check/test.Is it the ups that's faulty or the coming power from the building?
Thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:10 AM . Last Modified: 2024-03-12 04:41 AM
Do you know the exact model of the UPS? If it does not have it's own automatic or manual bypass (which only select 3000VA models provide) then you may need to move it to a different power source. For the future, a wrap around bypass panel (also called a service bypass panel) can provide power output if the UPS is not functioning properly.
Besides physically resetting the UPS, I can't think of anything remotely that could fix this because the inverter converts DC to AC and is a critical component of the UPS. Via the management card you could try controlling the output to turn it off/on but it sounds doubtful that it will change anything.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:10 AM . Last Modified: 2024-03-12 04:41 AM
Do you know the exact model of the UPS? If it does not have it's own automatic or manual bypass (which only select 3000VA models provide) then you may need to move it to a different power source. For the future, a wrap around bypass panel (also called a service bypass panel) can provide power output if the UPS is not functioning properly.
Besides physically resetting the UPS, I can't think of anything remotely that could fix this because the inverter converts DC to AC and is a critical component of the UPS. Via the management card you could try controlling the output to turn it off/on but it sounds doubtful that it will change anything.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.