Adding 2nd APC SmartUPS 1500 to a Windows server

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Adding 2nd APC SmartUPS 1500 to a Windows server
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:05 AM . Last Modified: ‎2024-02-29 10:19 PM

0 Likes
3
707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:05 AM . Last Modified: ‎2024-02-29 10:19 PM

Adding 2nd APC SmartUPS 1500 to a Windows server

I have a Windows server 2008 R2 running Powerchute Business Edition v9.2.   I have one SmartUPS 1500 plugged into the server via a USB cable and the Powerchute sees it fine and manages it fine.  I also have a 2nd SmartUPS 1500 that I want to add to it so I can see and manage the 2nd UPS.  I don't care about it being able to shutdown the server or not.  This server has redundant power supplies and each UPS is plugged into separate power sources with each power supply plugged into each separate UPS.

When I try to run the Device list configuration program, it never seems to even try to discover the new 2nd UPS.   The current UPS is listed in the device list using the server name.  I know the new 2nd UPS is being seen by the server, because it is listed in the computers device manager list. 

When I run the PCBE it shows the existing hostname (servername) and shows just one device. Its the original UPS.  The 2nd UPS is not showing up.

How can I add this 2nd UPS so can manage the settings for this UPS?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:05 AM . Last Modified: ‎2024-02-29 10:19 PM

0 Likes
0
707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:05 AM . Last Modified: ‎2024-02-29 10:19 PM

Hi,

PowerChute Business Edition has 3 components Agent, Server, Console. The Agent is responsible for communications with the UPS. The Server gathers information from the Agents and for the free version the Server will gather information from up to 5 Agents. We also offer a 25 node version. the Console is the GUI. If you have 5 UPS you will need 5 Agents communicating with the UPS to be represented in the Server and you can only have 1 Agent running on a single OS at a time. 

For a redundant solution you will need network management cards and PowerChute Network Shutdown. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:05 AM . Last Modified: ‎2024-02-29 10:19 PM

0 Likes
0
707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:05 AM . Last Modified: ‎2024-02-29 10:19 PM

Hi,

Redundant UPS are not support in PowerChute Business Edition. If you want to utilize redundant UPS you should purchase network management cards for each UPS and run PowerChute Network Shutdown. PowerChute Network Shutdown supports redundant UPS as listed in Application Note 98. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:05 AM . Last Modified: ‎2024-02-29 10:19 PM

0 Likes
0
707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:05 AM . Last Modified: ‎2024-02-29 10:19 PM

Why then does PCBE state in the device configuration that it supports up to 5 devices?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:05 AM . Last Modified: ‎2024-02-29 10:19 PM

0 Likes
0
708
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:05 AM . Last Modified: ‎2024-02-29 10:19 PM

Hi,

PowerChute Business Edition has 3 components Agent, Server, Console. The Agent is responsible for communications with the UPS. The Server gathers information from the Agents and for the free version the Server will gather information from up to 5 Agents. We also offer a 25 node version. the Console is the GUI. If you have 5 UPS you will need 5 Agents communicating with the UPS to be represented in the Server and you can only have 1 Agent running on a single OS at a time. 

For a redundant solution you will need network management cards and PowerChute Network Shutdown. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of