Actual UPS efficiencies don't match factory claims...?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Actual UPS efficiencies don't match factory claims...?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 05:58 AM . Last Modified: ‎2024-03-19 12:26 AM

0 Likes
4
1280
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:58 AM . Last Modified: ‎2024-03-19 12:26 AM

Actual UPS efficiencies don't match factory claims...?

I'm having trouble understanding the Factory/Manufacturers' claims on UPS efficiency.  All that I have seen claim min-90% efficiency of their UPS systems running in full dual-conversion mode.  However, what I am seeing in Actual efficiency (Amps out divided by Amps in) is in the low to mid 80% range.  Anybody have any clue why?  Or, how does APC actually "measure" their efficiency that allows them to claim ~95% efficiency starting at ~45% load.

For example, here locally we are being provided clean power by a bank of 5 APC MGE EPS 8000 625kva, 480v UPS.  They are connected to a common buss and are in an N+1 setup.

The average loading of the individual UPSs is 40-45%.  Based on an APC document I found online, these units should be 90% efficient starting at 20% load, with a peack efficiency of ~95% from 40-70% load.

However, what we are Actually seeing in production is Amps Out divided by Amps In = ~80%. 

I've seen elsewhere where KW Out/In is normally used for efficiencly calculations...but I can't see how that would make any significant difference?

Another, older, Liebert 750kva UPS we have is currently only loaded about 20-25%, and its measured Amps In/Out efficiency is ~85%...which I would expect with such a light loading.

A year old Eaton 550kva (2x 275kva) we recently looked at showed a similar 85% efficiency at ~35% load.

I guess my real question is this:

How do manufacturers measure "UPS Efficiency" in order to get mid-90% ratings?

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-26 05:58 AM . Last Modified: ‎2024-03-19 12:25 AM

0 Likes
0
1279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:58 AM . Last Modified: ‎2024-03-19 12:25 AM

You want W (or kW) for your efficiency calculation, not kVA. Watts are real power.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-26 05:58 AM . Last Modified: ‎2024-03-19 12:25 AM

0 Likes
0
1279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:58 AM . Last Modified: ‎2024-03-19 12:25 AM

Hi RT8,

I'm a little surprised you didn't measure 117% efficiency that way. If you figure the power factor of loads is 0.85 or so, and the UPS input is power factor corrected, then input_amps = output_amps*0.85 => output/input = 1/0.85 = 117%.

So yeah, there's a difference between W and A 🙂

I think of it like this: power is current * voltage, and that's sort of like you need both workers and available tasks to get work done. Both workers and available tasks go up and down with time. If they coincide, lots of work gets done. If you have workers when you don't have tasks and vice versa, no work gets done. So just measuring your average amount of workers and your average amount of tasks available can be misleading. Watts is like measuring the average amount workers who have tasks, while amps is like measuring the average amount of workers.

Even measuring volts or amps alone can get a bit tricky. Cheaper equipment assumes the standard ebb and flow of AC electricity. True-RMS meters make no such assumptions.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:58 AM . Last Modified: ‎2024-03-19 12:25 AM

0 Likes
0
1279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:58 AM . Last Modified: ‎2024-03-19 12:25 AM

Schneider Electric measures UPS efficiency according to the procedures specified by IEC 62040-3 Ed. 2 and/or ENERGY STAR for UPS version 1.0.  Both standards are similar in that they measure at 100%, 75%, 50% and 25% balanced resistive (PF=1.0) load, with nominal voltage and frequency input, at a temperature near 25ºC, with a fully charged or disconnected battery (to represent steady state conditions). The IEC standard defines efficiency as the ratio of power out to power in. ENERGY STAR calculates efficiency as the ratio of energy out over energy in. Transformerless UPSs and newer server power supplies have power factor corrected inputs which typically achieve power factors of 0.95 or greater when operating at > 25% load.

Some of the UPSs you mentioned may have input power factors substantially below 0.95, resulting in additional current flow without additional power flow. Your load may not have have a high power factor either. Measuring power accurately requires a true RMS power meter capable of measuring voltage and current simultaneously

In summary, you can't determine efficiency if you only know voltages and currents. You need to know input power (or energy) and output power (or energy).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 05:58 AM . Last Modified: ‎2024-03-19 12:25 AM

0 Likes
0
1279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:58 AM . Last Modified: ‎2024-03-19 12:25 AM

Angela N.

Thanks!

The vast majority of the load on the 5x APC string is predominantly computers, most of which have a PF in the high .9s.

I have no idea about the PF of the 3 UPSs I mentioned.

Ok, so now I need to collect input & output KW?  or KVA?  Which one is considered "power"?

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-26 05:58 AM . Last Modified: ‎2024-03-19 12:25 AM

0 Likes
0
1280
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:58 AM . Last Modified: ‎2024-03-19 12:25 AM

You want W (or kW) for your efficiency calculation, not kVA. Watts are real power.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.