Accuracy of runtime chart for SUA2200

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Accuracy of runtime chart for SUA2200
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 04:50 AM . Last Modified: ‎2024-03-08 04:01 AM

0 Likes
5
1853
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:50 AM . Last Modified: ‎2024-03-08 04:01 AM

Accuracy of runtime chart for SUA2200

I have a requirement to run an approx. 150w load for 3+ hours in case of power failure. According to the runtime chart on the APC site the SUA2200 looks to be just what i need. However, from looking at the runtimes for other products in the chart i'm worried that the entry for the SUA2200 may mistakenly be a duplicate of the SUA3000 data. e.g. why is there such a huge jump in runtimes between the SUA1500 and SUA2200 products but no real difference between the latter and the SUA3000 runtimes ? I don't want to find out after purchase that i'll only get about 2.5 hours from unit.

Anyone know if the SUA2200 figures are accurate ?

Also, anyone know how many watts the SUA2200 will use when fully charged and with mains power still on ?

/splotch

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-30 04:50 AM . Last Modified: ‎2024-03-08 04:01 AM

0 Likes
0
1853
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:50 AM . Last Modified: ‎2024-03-08 04:01 AM

splotch wrote:
Just trying to get my head around this.The SUA3000 has a max load of 2.7kw and can carry this for 6 mins whereas the SUA2200 has a max load of 1.98kw and can carry this for 7 minutes but you're saying they still have identical battery capacity ?

Yes. You have 2.7kw on a battery, which gives you 6 minutes. Then you have the same battery, and you put 1.98kw on it, and you have 7 minutes of runtime. You put more load on the first example, so the runtime is less. If you run our runtime calculator on the product website under "Compare Models" and input 1.98kw you will see that both have a 7 minute runtime. They use the same battery, the same battery charging technology, and the charger power for both the SUA3000 and SUA2200 is the same: 271 watts. Because they use the same battery, the reaction the battery has to x amount of draw during a power loss is going to be the same, it just so happens that the SUA3000 is capable of pulling more load...

In regards to UPS draw, all we have is the charger spec which is 271 watts. The additional draw from LEDs, an idle smartslot, etc. might be...20, 25 watts or around there. That's all we can give in terms of power draw. When idle I would imagine the draw would be far under the 271 watt battery charger limit. We don't have a longterm measurement of power draw since that would be highly dependent on customer site conditions, environment, etc.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-30 04:50 AM . Last Modified: ‎2024-03-08 04:01 AM

0 Likes
0
1853
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:50 AM . Last Modified: ‎2024-03-08 04:01 AM

The SUA1500 and SUA2200 use entirely different batteries, hence a large difference in runtime. The SUA2200 and SUA3000 share the same battery type, therefore on-battery capacity, which explains the runtime readings. The readings for the SUA2200 are accurate for whatever wattage you are providing it.

The draw from an SUA2200 is minimal when fully charged and online with no load. I cannot give exact figures but assuming that there is no charging needed, no accessory installed in the SmartSlot, and no load, the draw necessary just to power the system PCB, LEDs, etc. is going to be far under an amp.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:50 AM . Last Modified: ‎2024-03-08 04:01 AM

0 Likes
0
1853
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:50 AM . Last Modified: ‎2024-03-08 04:01 AM

Just trying to get my head around this.The SUA3000 has a max load of 2.7kw and can carry this for 6 mins whereas the SUA2200 has a max load of 1.98kw and can carry this for 7 minutes but you're saying they still have identical battery capacity ?

Anyone know how many watts the SUA2200 will draw while waiting to be called into action ?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:50 AM . Last Modified: ‎2024-03-08 04:01 AM

0 Likes
0
1853
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:50 AM . Last Modified: ‎2024-03-08 04:01 AM

Splotch,

The battery charger in the SUA2200 is 271W. So at max if the UPS is idle w/ no load, it would use 271W if the battery were being charged, and obviously some amount less if simply idle and trickle charging the battery.

-Mike

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 04:50 AM . Last Modified: ‎2024-03-08 04:01 AM

0 Likes
0
1853
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:50 AM . Last Modified: ‎2024-03-08 04:01 AM

I should clarify regarding my power consumption question, I'm trying to estimate how much power will be consumed over a period of time (e.g. month or year) in the best case scenario where the UPS is fully charged and never called into action, which is why i'm asking for the watts used by the SUA2200 when fully charged with the mains supply still on.
i.e. i'm trying to estimate the best case additional electricity cost of inserting this UPS into an existing system for which i already know the running cost, so it's this negligible draw while trickle charging that i need to know.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-30 04:50 AM . Last Modified: ‎2024-03-08 04:01 AM

0 Likes
0
1854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 04:50 AM . Last Modified: ‎2024-03-08 04:01 AM

splotch wrote:
Just trying to get my head around this.The SUA3000 has a max load of 2.7kw and can carry this for 6 mins whereas the SUA2200 has a max load of 1.98kw and can carry this for 7 minutes but you're saying they still have identical battery capacity ?

Yes. You have 2.7kw on a battery, which gives you 6 minutes. Then you have the same battery, and you put 1.98kw on it, and you have 7 minutes of runtime. You put more load on the first example, so the runtime is less. If you run our runtime calculator on the product website under "Compare Models" and input 1.98kw you will see that both have a 7 minute runtime. They use the same battery, the same battery charging technology, and the charger power for both the SUA3000 and SUA2200 is the same: 271 watts. Because they use the same battery, the reaction the battery has to x amount of draw during a power loss is going to be the same, it just so happens that the SUA3000 is capable of pulling more load...

In regards to UPS draw, all we have is the charger spec which is 271 watts. The additional draw from LEDs, an idle smartslot, etc. might be...20, 25 watts or around there. That's all we can give in terms of power draw. When idle I would imagine the draw would be far under the 271 watt battery charger limit. We don't have a longterm measurement of power draw since that would be highly dependent on customer site conditions, environment, etc.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore