APC7921 Password Reset

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC7921 Password Reset
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:02 PM

0 Likes
23
8163
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:02 PM

APC7921 Password Reset

Hi,

I tried changing the password via web interface (from apc/apc), and seems i must have had a typo (great use of singular form field for password change :S)

I've tried factory resetting (10 seconds held in, release, 1 second held in). However, this isn't working, in that apc/apc doesn't work after i do this.

I don't have a serial cable, and it seems a RJ12 cable here in the UK is near impossible to get hold of, and i dont have a laptop with a serial port anyway.

What are my options?

Many thanks,

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 07:09 AM . Last Modified: ‎2024-03-04 11:00 PM

0 Likes
0
8160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:09 AM . Last Modified: ‎2024-03-04 11:00 PM

Angela,

Do you have a direct link to the .bins? I can only find a "Network Management Card v3.7.4 RPDU Firmware Executable" which gives me a .exe that i cannot open on my linux machines 😮

thanks!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 23
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:02 PM

0 Likes
0
8158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:02 PM

Hi,

I am not sure where you came across that "factory reset" procedure you did but it does not apply to this device. AP7XXX series PDUs don't have any procedure that involves holding down their reset button.

If you forgot the administrator password, resetting it will require you to connect locally to it via a serial cable to reset it. There is no way to reset it remotely unfortunately which would also be a security concern for many.

The procedure you'd want to find would involve getting a 940-0144 cable and then refer to the NMC1 instructions here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156075 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:02 PM

0 Likes
0
8158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:02 PM

Hi Angela, thanks for the quick reply.

I found the procedure on google, and there is even a youtube video of the process so thats kind of odd. The status lights even react as pointed out in these various posts.

If serial cable is really the only way forward, where can i source one in the UK? I can't find one on ebay or anywhere else, and definitely not one i can actually use with my laptop..

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:02 PM

0 Likes
0
8159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:02 PM

I am based in the US so I am not sure where it may be available in the UK. Local support there may know. I have to believe this cable is on ebay. Did you try searching 940-0144 and 940-0144A? Our service spare part number for it is 0J-940-0144A.

I see it on UK ebay? http://www.ebay.co.uk/sch/i.html?_nkw=940-0144A&ssPageName=GSTL Sounds like you may also need a serial to USB adapter as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:02 PM

0 Likes
0
8159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:02 PM

Angela,

Amazing, thankyou. Would this adapter suffice? and will this work under linux?

http://www.ebay.co.uk/itm/USB-2-0-TO-RS232-SERIAL-DB9-9-PIN-ADAPTER-CABLE-GPS-PDA-/400748245338?pt=L...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:02 PM

0 Likes
0
8159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:02 PM

I am not sure on that one. You'll just want to make sure the vendor makes a Linux driver for it. The adapter I use (because I also don't have a serial port on my work PC) is this one -> http://www.radioshack.com/gigaware-usb-to-serial-cable/2603487.html and I've gotten it to work on Windows and Mac OS X. I am not sure if it is available in your area but it is the only one I can personally vouch for.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:02 PM

0 Likes
0
8159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:02 PM

Angela,

Thanks for the help prior.

I now have the official APC part with a converter that uses the linux driver "ch341". I'm using GTKTERM with the config settings 9600 8-N-1. However, the screen just stays blank. What is the correct procedure to reset password? Should i be seeing something on screen prior to pressing the reset button?

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:01 PM

0 Likes
0
8159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:01 PM

Hi John,

So you have no flow control set, correct, on the port speed? That should be set to none. You have the RJ-12 end of 940-0144 connected to the PDU's serial port, then the DB-9 end connected to your USB to serial adapter. If everything is working properly, you should just need to verify scroll lock on your keyboard is off/disabled and press enter several times to start talking to the PDU. Then, you do the button pressing stuff in the article and then log in with apc/apc temporarily to get to the system menu to change the credentials to whatever you'd like.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:01 PM

0 Likes
0
8159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:01 PM

Yes to everything you said regarding the setup.

You said press enter to start talking to the PDU, should I get a response to this? Pressing enter I just get the same cursor, nothing changes. Or do I only get a username prompt once reset button is pressed?

do I need network cable disconnected for this? Other outlets?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:01 PM

0 Likes
0
8159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:01 PM

Hi John,

Yes, it should provide a prompt that says User Name: and yes, ethernet cable can remain connected and the aforementioned prompt should come up without pressing the reset button. What tool are you using for terminal access? Is it set to use VT100?

Do you have any other APC device or other serial device we can try this on? I take it not?

Have you rebooted after installing the driver for this serial to USB adapter? (I am just recalling what I had to go through to get mine working on Mac OS X.)

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:01 PM

0 Likes
0
8159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:01 PM

Angela,

I'm using GTKTERM and have also tried minicomputer (Linux based software).

I've not come across VT100 in config so I will look for this.

I didn't have to install a driver for my converter, it automatically used ch341 which is in Linux kernel, if all of the above turns out that it doesn't work still then I think driver debugging or maybe buying another converter is an option to rule this out.

I don't believe I have another serial port device, though i do have a rackmount NAS and switch that possibly do so I will check them out as well.

I really appreciate the advice, I will go over some things again and update you, hopefully with a positive result!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:01 PM

0 Likes
0
8159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:01 PM

oh sorry! I didn't pick up that GTKTERM was the name of the program previously but I had read that.

You're welcome. Yes, VT100 refers to the type of terminal emulation so I'd see if you see that somewhere and make sure its not set to something else. I used "serial tools" on Mac and on Windows I am always using PuTTy or HyperTerminal. I know some people use TeraTerm too.

So yeah, port speeds, scroll lock off, good cable, good driver on the coverter, correct COM port selection in GTKTERM..that is what is going through my mind.

I'll look forward to your update. I hope we can get this working!

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:01 PM

0 Likes
0
8159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:01 PM

Does your USB-to-serial adapter have any indicator LEDs on it? The one I use has 2 LEDs, one showing data from computer -> serial and another for serial -> computer. If yours has something similar, you can at least confirm that your terminal program is talking to the serial adapter. If it doesn't have LEDs, you could carefully jumper pins 2 and 3 together on the 9-pin serial end of the USB adapter (they should be numbered), being careful to not short them to other pins or the metal shell of the connector. You should then be able to see every character you type displayed on the screen.

If you test the adapter in this manner and it doesn't work, you may be using the wrong port (normally something like /dev/ttyXX) or something else may have accessed the port in exclusive mode (for example, getty may be listening on it in case someone tries to log in). Other possibilities include a bad adapter, incorrect driver, etc.

If the adapter tests out OK, then you may be using the wrong baud rate (9600 is common, some APC gear used 2400 or 19200). If your terminal program doesn't allow you to change it, you could try the stty command, normally "stty -f /dev/ttyXX speed 9600", where XX is the port your adapter shows up as.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:01 PM

0 Likes
0
8159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:08 AM . Last Modified: ‎2024-03-04 11:01 PM

Hi Angela,

I know its been a very long time but i never did sort this issue!

I've taken some screenshots of the config from "minicom", as with GTKTERM i'm just left with a flashing cursor:

http://imgur.com/pemq2U6

VT102 is shown, i can't see VT100 anywhere just ANSI

Here is a picture of my adaptor, not sure if it helps, there is no led:

http://imgur.com/CBlvMBx

I really would love to get access back again now as i have many more things in my rack and want to monitor usage, which is why i bought the network PDU in the first place!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 07:09 AM . Last Modified: ‎2024-03-04 11:01 PM

0 Likes
0
8159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:09 AM . Last Modified: ‎2024-03-04 11:01 PM

Hi John,

I am not too familiar with Minicom but did a search and see you're basically doing the same thing as outlined here -> http://bigunix.blogspot.com/2009/09/how-to-configure-apc-pdu-using-minicom.html?_sm_au_=iHV724PNSZQT... 

At this point, I don't think it'd hurt to try a baud rate of 2400 to see if got changed from default of 9600. The others to give a quick try just incase would be 19200 and 38400.

Don't know what Terry things but looking at the adapter, I wouldn't know if anything was wrong there unfortunately.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 07:09 AM . Last Modified: ‎2024-03-04 11:01 PM

0 Likes
0
8159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:09 AM . Last Modified: ‎2024-03-04 11:01 PM

Ok I'll give the other rates a go and I've also bought another adapter to see if that's the issue, will keep you posted

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 07:09 AM . Last Modified: ‎2024-03-04 11:01 PM

0 Likes
0
8159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:09 AM . Last Modified: ‎2024-03-04 11:01 PM

New converter turned up in double fast time and it worked!

Thanks for all the help.

One last thing before the thread is done with, how do i find the current firmware version on this device?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 07:09 AM . Last Modified: ‎2024-03-04 11:01 PM

0 Likes
0
8159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:09 AM . Last Modified: ‎2024-03-04 11:01 PM

It is displayed when you log in on the top right. You'll see Network Management Card AOS 3.9.0 and Rack PDU APP 3.7.4 (hopefully). Alternatively, it is displayed under System->About menu I believe.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 07:09 AM . Last Modified: ‎2024-03-04 11:01 PM

0 Likes
0
8159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:09 AM . Last Modified: ‎2024-03-04 11:01 PM

Its in neither place! I'll assume i have a very old firmware then!

I really want to make sure i upgrade correctly as to not have a repeat performance as last time. Is it possible its not visible via the UI at all in very old versions?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 07:09 AM . Last Modified: ‎2024-03-04 11:01 PM

0 Likes
0
8159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:09 AM . Last Modified: ‎2024-03-04 11:01 PM

It should be there. Even the predecessor to the product had it in these menus. At least on the top right after you log in. Can you share what  you do see if it is not similar to below in some way?

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 07:09 AM . Last Modified: ‎2024-03-04 11:01 PM

0 Likes
0
8158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:09 AM . Last Modified: ‎2024-03-04 11:01 PM

Ah, sorry i thought you mean't WebUI. 

Yes i have this via telnet "v2.6.4"

Can i go straight to latest firmware from this version and it can be done via telnet?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 07:09 AM . Last Modified: ‎2024-03-04 11:00 PM

0 Likes
0
8158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:09 AM . Last Modified: ‎2024-03-04 11:00 PM

Hi John,

Ah, OK. That is not too old. And yes, you can go straight to AOS 3.9.0/rpdu APP 3.7.4. Only AOS 1.X.X has an upgrade path requirement to get to v3.X.X so that does not apply to you.

Telnet protocol doesn't support file transfer. You'll want to use FTP, XMODEM (serial cable - a very slow last resort), or SCP. Sounds like FTP will be easiest. Once you download the firmware, you'll get three .bin files. AOS 3.9.0, AOS 2.0.2, and rpdu 3.7.4. Get rid of AOS 2.0.2 as you won't need it and then follow the FTP/NMC1 instructions here -> http://www.schneider-electric.us/support/index?page=content&country=US〈=en&locale=en_US&id=FA156047 

Let me know if you have any questions before starting.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 07:09 AM . Last Modified: ‎2024-03-04 11:00 PM

0 Likes
0
8161
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 07:09 AM . Last Modified: ‎2024-03-04 11:00 PM

Angela,

Do you have a direct link to the .bins? I can only find a "Network Management Card v3.7.4 RPDU Firmware Executable" which gives me a .exe that i cannot open on my linux machines 😮

thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

ezhyg
ezhyg
Cadet

Posted: ‎2024-07-08 09:15 PM

0 Likes
0
5016
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-08 09:15 PM

Hi John,

Can you Help me? Big thanks

АР9530

541339E08022

 

mac:

00C0B7B5A8C5

IMG_5084.jpeg

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore