APC X3000 Garbled Display After Battery Swap

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC X3000 Garbled Display After Battery Swap
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:06 AM . Last Modified: ‎2024-03-15 06:05 AM

0 Likes
2
748
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:06 AM . Last Modified: ‎2024-03-15 06:05 AM

APC X3000 Garbled Display After Battery Swap

Greetings,

The SMX3000RMLV2UNC in our server room has a odd issue after swapping a dead battery for a new one. Before I swapped it out I noticed the Smart-UPS Display was displaying garbled text, the information on the display was very hard to read. I chalked it up to the faulty battery and went about swapping in the new one. The screen was still garbled and I attempted to set the battery install date but it didn't seem to take.

After letting it charge for 24 hours, I returned to the server room and noticed that the battery fault light was still red, the display did not correct itself and with the new battery installed it is still chirping that it needs a replacement. I attempted a re-seat of the new battery to see if that helped but alas, nothing seems to be correcting the issue.

Has anyone experienced this when swapping out a faulty battery for a new one? I have replaced a battery in this unit twice before with no issues. The unit was purchased in 2013.

Any help would be appreciated. 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:06 AM . Last Modified: ‎2024-03-15 06:05 AM

0 Likes
0
748
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:06 AM . Last Modified: ‎2024-03-15 06:05 AM

Hi Ty - 

I do recommend Matt's suggestions, but more likely than not you have a faulty display. If you are using a Network Management card you should be able to do everything you need to do from the web interface even if the LCD display is non functional (assuming the buttons still work ok). The UPS is well out of warranty at this point, but it should still have some life in it, just with limited functionality.

thanks

Liam

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:06 AM . Last Modified: ‎2024-03-15 06:05 AM

0 Likes
0
748
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:06 AM . Last Modified: ‎2024-03-15 06:05 AM

Hi Ty

A couple of things worth trying.

1. Braindead the UPS 

https://infocenter.schneider-electric.com/InternalIC/index?page=content&id=FA156611&actp=search&view...

If that doesn't resolve the problem...

2. Updating the UPS firmware or reflashing it with the current firmware if it is already on the latest may help.

https://infocenter.schneider-electric.com/InternalIC/index?page=content&id=FA281865&actp=search&view...

Regards

Matt

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:06 AM . Last Modified: ‎2024-03-15 06:05 AM

0 Likes
0
749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:06 AM . Last Modified: ‎2024-03-15 06:05 AM

Hi Ty - 

I do recommend Matt's suggestions, but more likely than not you have a faulty display. If you are using a Network Management card you should be able to do everything you need to do from the web interface even if the LCD display is non functional (assuming the buttons still work ok). The UPS is well out of warranty at this point, but it should still have some life in it, just with limited functionality.

thanks

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore