Posted: 2021-06-28 10:06 AM . Last Modified: 2024-03-15 06:05 AM
We have a Symmetra LX 16kVA N+1 unit that has three SYAPD1s on the back. Up until now we have only populated the L5-20s and left the L14-30 outlet vacant. We now have a new storage array that will need the L14-30 outlet. As long as we are not exceeding the amperage on the system, we can use all three plugs on these power distribution panels correct?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:06 AM . Last Modified: 2024-03-15 06:04 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:06 AM . Last Modified: 2024-03-15 06:04 AM
is correct, all 3 can be used at the same time
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:06 AM . Last Modified: 2024-03-15 06:04 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:06 AM . Last Modified: 2024-03-15 06:04 AM
is correct, all 3 can be used at the same time