Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:06 AM . Last Modified: 2024-03-15 06:05 AM
We have a Symmetra LX 16kVA N+1 unit that has three SYAPD1s on the back. Up until now we have only populated the L5-20s and left the L14-30 outlet vacant. We now have a new storage array that will need the L14-30 outlet. As long as we are not exceeding the amperage on the system, we can use all three plugs on these power distribution panels correct?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:06 AM . Last Modified: 2024-03-15 06:04 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:06 AM . Last Modified: 2024-03-15 06:04 AM
is correct, all 3 can be used at the same time
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:06 AM . Last Modified: 2024-03-15 06:04 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:06 AM . Last Modified: 2024-03-15 06:04 AM
is correct, all 3 can be used at the same time
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.