Posted: 2021-06-28 10:05 AM . Last Modified: 2024-03-15 06:05 AM
I have the above UPS where the batteries have completely drained; the terminal reads 6V. Can this value prevent the UPS from starting as this one does when plugged into AC outlet?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:06 AM . Last Modified: 2024-03-15 06:05 AM
Thanks Matt I have resolved the problem after replacing batteries.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:05 AM . Last Modified: 2024-03-15 06:05 AM
Hi mntambo
Yes, the SURT UPS range require a certain battery voltage to start up.
The more recent SRT range is able to start up without battery.
Regards
Matt
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:06 AM . Last Modified: 2024-03-15 06:05 AM
Thanks Matt I have resolved the problem after replacing batteries.