APC UPS 3000 RM - Battery Module wont come out

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC UPS 3000 RM - Battery Module wont come out
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 11:42 PM . Last Modified: β€Ž2024-03-11 04:35 AM

0 Likes
8
10623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 11:42 PM . Last Modified: β€Ž2024-03-11 04:35 AM

APC UPS 3000 RM - Battery Module wont come out

Anyone have any problems with removing the battery module for an APC 3000RM series UPS. I removed the three screws, but the module can only be shimmied left/right and up/down a bit. Anyone experience this before? Cant imagine what's locking it up. I even removed the top case cover and I'm stuck.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 3000
  • apc
  • battery
  • can't
  • Hi everyone
  • i have a APC UPS model SMT3000RMI2UC connected to a server i have a battery probleme i want to change the batterys without senteing off the server how i do it
  • module
  • remove
  • replacement
  • rm
  • stuck
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 11:42 PM . Last Modified: β€Ž2024-03-11 04:35 AM

0 Likes
1
10621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 11:42 PM . Last Modified: β€Ž2024-03-11 04:35 AM

Thanks for the advice. The flat blade screwdriver worked well getting the two batteries out of the frame. Swapped connectors, reinstalled, and back in business.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 11:42 PM . Last Modified: β€Ž2024-03-11 04:35 AM

0 Likes
0
10624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 11:42 PM . Last Modified: β€Ž2024-03-11 04:35 AM

I've dealt with this situation numerous times. The first thing to try is unplug the battery string completely and try using a large straight blade screwdriver to pry on the battery casing from the left and right sides - lever the screwdriver against the metal ups chassis casing to the left and right of the battery opening alternately to wiggle it out. If the screwdriver tip is sharp enough it will bite into the plastic of the battery and get extra grip. Don't worry if you crack the case of the battery it will not cause a problem (re leaks or shorts) as the batteries are toast anyway. If that doesn't work your only choice is to unplug the battery, power down the ups, remove it from the rack, let the UPS sit for a couple of days to drain any charge on the capacitors and then take the top off the UPS and get the batteries out one by one possibly removing some interior screws to losen the battery compartment walls. Some are riveted though!

Good luck,

Dave

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 11:42 PM . Last Modified: β€Ž2024-03-11 04:35 AM

0 Likes
0
10622
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 11:42 PM . Last Modified: β€Ž2024-03-11 04:35 AM

Sounds like the battery has become "swollen" for any of a variety of issues including an extended overcharge condition, etc. It's going to take sheer physical force to pry the battery out.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 11:42 PM . Last Modified: β€Ž2024-03-11 04:35 AM

0 Likes
0
10626
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 11:42 PM . Last Modified: β€Ž2024-03-11 04:35 AM

what i would suggest if you haven't done it already is allow the battery to cool off and make sure it is not continuing to charge. you should power down the UPS completely (which means your attached load too needs to be off) and then disconnect the battery. a fan also might be helpful on the battery to cool it down and maybe shrink it a bit enough to wiggle it out of there.

before i say all that actually - is the battery even warm? how old is it?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 11:42 PM . Last Modified: β€Ž2024-03-11 04:35 AM

0 Likes
0
10627
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 11:42 PM . Last Modified: β€Ž2024-03-11 04:35 AM

Thanks guys for the ideas thus far. The battery is quite old (3 years). I have not disconnected it for more than 15 minutes at a time, since doing so leads to it chirping every few seconds, which is annoying. Is there a way to turn this off, or to disable the 1 minute chirping every 5 hour cycle until I get this resolved?

It doesn't feel swollen so much as though something is blocking it. As I mentioned, I can shimmy it an eighth of an inch left/right and up/down at the front, but it has only about an eighth of an inch pull before it locks, and I've pulled the thing pretty dang hard. I'm thinking of shutting down the servers its powering and pulling it out of the rack, but that's a lot of inconvienience, headache and work that I'm trying to avoid.

Classic case of a 10 minute job turning into something else entirely 😞

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 11:42 PM . Last Modified: β€Ž2024-03-11 04:35 AM

0 Likes
1
10622
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 11:42 PM . Last Modified: β€Ž2024-03-11 04:35 AM

Thanks for the advice. The flat blade screwdriver worked well getting the two batteries out of the frame. Swapped connectors, reinstalled, and back in business.

Reply

Link copied. Please paste this link to share this article on your social media post.

SteveSJ
SteveSJ
Cadet

Posted: β€Ž2022-04-20 09:18 AM

In response to Anonymous user
0 Likes
0
10329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2022-04-20 09:18 AM

I can confirm that the flat blade screwdriver works.  I started out side to side but also used it on the bottom.  Takes A LOT of patience.  If it doesn't work at first, take a break and come back to it later.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

youcefkerri
youcefkerri
Cadet

Posted: β€Ž2025-02-02 02:28 AM

0 Likes
1
1438
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-02-02 02:28 AM

Hi everyone , i have a APC UPS model : SMT3000RMI2UC with battery probleme ? i want to ask you if this model have a Bypass mode to let me change the battery without turning off the UPS ? and if yes , how to acess to this mode ( bypass) 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Janeway Teken
Janeway

Posted: β€Ž2025-02-03 05:47 AM

In response to youcefkerri
0 Likes
0
1428
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2025-02-03 05:47 AM

The unit is hot swappable so no need to bypass anything. Just remove the screws, unplug the connector, remove the battery cartridge.

 

Do the reverse with the new battery cartridge. Wait for the system to declare a battery fault.

 

The system will prompt you to affirm if the battery cartridge has been replaced so toggle from No to Yes!

 

Hit save / enter . . . 

Once the battery is 100% State of Charge (SOC). Manually initiate a Self Test and let pass. Let the battery recover to 100% SOC.

 

Complete the process by manually initiating a Battery Calibration with at least 30% attached load. Let complete and battery return to 100% SOC.

 

The displayed operational runtime will now be more accurate as it relates to the attached load.

 

Questions Ask . . . πŸ‘

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of