APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:44 PM . Last Modified: 2024-03-01 12:28 AM
Hi All,
SRCPK001; what does it mean about paralleling? If i have two 5kVA ups, sum capacity like 10kVA else ?
Thanks for all
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:44 PM . Last Modified: 2024-03-01 12:27 AM
Please share complete operating procedure of RC paralleling Kit,
>If we turn OFF ups 1 input breaker, why ups 2 also turn into battery mode?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:44 PM . Last Modified: 2024-03-01 12:28 AM
Hi,
I found this brochure: http://www.apcmedia.com/salestools/SKAY-9LVKKH/SKAY-9LVKKH_R0_EN.pdf
It seems to indicate the parallel kit provides redundancy, rather than increased/doubled capacity.
Parallel redundancy — Two Units can be placed into a redundant configuration to improve availability (5 – 10 kVA only).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:44 PM . Last Modified: 2024-03-01 12:28 AM
This is for double capacity or just load protect ? Please tell me application for this. If I have 2 5kVA ups with this unit, what can do system ? What is the benefit with this product?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:44 PM . Last Modified: 2024-03-01 12:27 AM
What I tried to explain is that this particular kit is for redundancy/fault tolerance. It does not double the load capacity. With (2) 5kVA UPSs, if one fails/faults/goes down, the other one will still support the load with no interruption. The total load capability is still 5kVA.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:44 PM . Last Modified: 2024-03-01 12:27 AM
Im so happy from your explain Angela, When I see parraleling kit, I think, it does it mean like 3P UPSs paralleling operation.
Now All things clean. This is for If I have 2 x 5kVA UPS, no intteruption working for one at the any problems. Thanks your answer.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:44 PM . Last Modified: 2024-03-01 12:27 AM
No problem and yes, I know the 3 phase paralleling kits work a little differently so I am happy to help clarify.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:44 PM . Last Modified: 2024-03-01 12:27 AM
Please share complete operating procedure of RC paralleling Kit,
>If we turn OFF ups 1 input breaker, why ups 2 also turn into battery mode?
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.