Posted: 2021-07-07 10:44 PM
This question was originally posted by Ahmet on APC forums on 5/20/2015
Hi All,
SRCPK001; what does it mean about paralleling? If i have two 5kVA ups, sum capacity like 10kVA else ?
Thanks for all
Posted: 2021-07-07 10:44 PM
This reply was originally posted by M.Adnan on APC forums on 5/18/2016
Please share complete operating procedure of RC paralleling Kit,
>If we turn OFF ups 1 input breaker, why ups 2 also turn into battery mode?
Posted: 2021-07-07 10:44 PM
This reply was originally posted by Angela on APC forums on 5/20/2015
Hi,
I found this brochure: http://www.apcmedia.com/salestools/SKAY-9LVKKH/SKAY-9LVKKH_R0_EN.pdf
It seems to indicate the parallel kit provides redundancy, rather than increased/doubled capacity.
Parallel redundancy — Two Units can be placed into a redundant configuration to improve availability (5 – 10 kVA only).
Posted: 2021-07-07 10:44 PM
This reply was originally posted by Ahmet on APC forums on 5/20/2015
This is for double capacity or just load protect ? Please tell me application for this. If I have 2 5kVA ups with this unit, what can do system ? What is the benefit with this product?
Posted: 2021-07-07 10:44 PM
This reply was originally posted by Angela on APC forums on 5/20/2015
What I tried to explain is that this particular kit is for redundancy/fault tolerance. It does not double the load capacity. With (2) 5kVA UPSs, if one fails/faults/goes down, the other one will still support the load with no interruption. The total load capability is still 5kVA.
Posted: 2021-07-07 10:44 PM
This reply was originally posted by Ahmet on APC forums on 5/21/2015
Im so happy from your explain Angela, When I see parraleling kit, I think, it does it mean like 3P UPSs paralleling operation.
Now All things clean. This is for If I have 2 x 5kVA UPS, no intteruption working for one at the any problems. Thanks your answer.
Posted: 2021-07-07 10:44 PM
This reply was originally posted by Angela on APC forums on 5/21/2015
No problem and yes, I know the 3 phase paralleling kits work a little differently so I am happy to help clarify.
Posted: 2021-07-07 10:44 PM
This reply was originally posted by M.Adnan on APC forums on 5/18/2016
Please share complete operating procedure of RC paralleling Kit,
>If we turn OFF ups 1 input breaker, why ups 2 also turn into battery mode?