APC Smart-UPS 1000 LCD (SMT1000I) - Can't access Display Power-Saving mode

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC Smart-UPS 1000 LCD (SMT1000I) - Can't access Display Power-Saving mode
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:36 AM . Last Modified: ‎2024-03-11 12:57 AM

0 Likes
4
898
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:36 AM . Last Modified: ‎2024-03-11 12:57 AM

APC Smart-UPS 1000 LCD (SMT1000I) - Can't access Display Power-Saving mode

The Operation Manual manual says:

Standard menus items are: Status, Configuration, Test & Diags.

Items in Configuration submenu:

• Language
• Local power quality: Good, Fair, Poor
• Choose Standard or Advanced menus
• LCD Display mode: Always On or Power-Saving
• Audible alarms
• Reset to Factory Defaults

But - I can't access LCD Display mode - it is missing.

The item is missing as well as I switch to Advanced Menus display mode.

How can I make this hidden item available (I want to switch the display into Power-Saving mode)?

-----------------------------------------
UPS Firmware 1: 05.0
UPS Firmware 2: COM 02.1

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:36 AM . Last Modified: ‎2024-03-11 12:56 AM

0 Likes
0
898
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:36 AM . Last Modified: ‎2024-03-11 12:56 AM

If you think UPS Network Management Card 2 (AP9630 or AP9631), I do not have.
I have only a serial interface cable supplied with accessories - 9 pin/RJ45.
My PC has native COM port, and PCI expansion card with a serial port as well.

About the risk of incorrect firmware upgrade - I know what does it mean, of course.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:36 AM . Last Modified: ‎2024-03-11 12:57 AM

0 Likes
0
898
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:36 AM . Last Modified: ‎2024-03-11 12:57 AM

Hi Roman,

What we can try doing here is updating your UPS to the current firmware release and then check if that feature would show up. The last time that I have talked to your product specialist I was told that few models has it and it could be part of the latest firmware.

With regards to updating the firmware, it can be done with the help of our Technical Support Team. Please do give them a call.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:36 AM . Last Modified: ‎2024-03-11 12:57 AM

0 Likes
0
898
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:36 AM . Last Modified: ‎2024-03-11 12:57 AM

Thanks for the reply, Jonathan - I just wrote for technical support.
Could I make a firmware update myself - I am IT specialist?
Do I need any special equipment?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:36 AM . Last Modified: ‎2024-03-11 12:56 AM

0 Likes
0
898
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:36 AM . Last Modified: ‎2024-03-11 12:56 AM

With regards to the equipment, it depends on what firmware would be loaded. There are firmwares that can be loaded using the network management card and the others would be by using the serial cable that came with the SMT/SMX. Using the second option, you need to have a PC with an available serial port. Then only the tech has a copy of the firmware and it is really a rule that in doing the upgrade the customer should be on the phone while doing the upgrade and this is to ensure that every step is done correctly. Incorrect flashing of the firmware could lead to UPS failure, it can brick the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:36 AM . Last Modified: ‎2024-03-11 12:56 AM

0 Likes
0
899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:36 AM . Last Modified: ‎2024-03-11 12:56 AM

If you think UPS Network Management Card 2 (AP9630 or AP9631), I do not have.
I have only a serial interface cable supplied with accessories - 9 pin/RJ45.
My PC has native COM port, and PCI expansion card with a serial port as well.

About the risk of incorrect firmware upgrade - I know what does it mean, of course.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore