
Posted: 2021-06-29 05:37 AM . Last Modified: 2024-03-13 12:47 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:37 AM . Last Modified: 2024-03-13 12:47 AM
APC Smart 1000VA(700W) crashed
Helloto all.yesterdaywhile I hadthe UPSon anda load of about100Wat one pointandjumped in witha bigbang, making me jumpa10Abreakerbefore theUPS.
Idisassembledit and founda diode(D21) witha while yousmoke.thestrange thing is thatnotskippedthe diodebutas if wehadputa wire betweenthe pins.
canan insect orspider thatwas wanderinginside?
here are the pictures:
on the motherboardtherewrote:LYNX2kVAMAIN BOARD
the model of theUPSis previousto the onethat is marketedtoday
ie: SUOL1000XLI
instead of the current:SURT1000XLI
wherethereis little differencein components.
SUOL1000XLI
SURT1000XLI
- Labels:
-
Smart-UPS & Symmetra LX | RM
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions

Posted: 2021-06-29 05:38 AM . Last Modified: 2024-03-13 12:47 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:38 AM . Last Modified: 2024-03-13 12:47 AM
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:38 AM . Last Modified: 2024-03-13 12:47 AM
Can you confirm what LEDs and if you're reading top to bottom or bottom to top?
0
0
0
0
0
above is how i look at the battery bar graph. Can you change the ones you see on to "1?"
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-29 05:38 AM . Last Modified: 2024-03-13 12:47 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:38 AM . Last Modified: 2024-03-13 12:47 AM
lightsso.all the othersare off.
but therea legendwiththeerror description?
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:38 AM . Last Modified: 2024-03-13 12:47 AM
There is but it is not public consumption
Also, this indicates a fan fault.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-29 05:38 AM . Last Modified: 2024-03-13 12:47 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:38 AM . Last Modified: 2024-03-13 12:47 AM
I would like tounderstand whythismight have happened.
andbecause it is nota fusewirewas placedat the inlet.Fortunatelydebreaker thatI had installed10AretrospectIcould seesmokeor fireworkswould jumpfincethemain25A.
Iusethe UPSaswell as inlive audiotosendthe audio mixeranddevicessensitive tovoltagefluctuationsorcalamenti.
ifwhathappened to meinthe geneduring the eveningI wasbadlyput.
at the timethe defectwas in the houseand I hadtheupsas wellinexternal bypassrelay. thatthe fall of theupsutilitieswerepoweredfrom the mains.
with this thingandnowI have littleconfidenceto taketheupsinaudioserivce.
anditmaywellhave beentheupsa littleolder andnotdouble-checkedby you.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-29 05:38 AM . Last Modified: 2024-03-13 12:47 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:38 AM . Last Modified: 2024-03-13 12:47 AM
Hi,
I am wondering if someone with this UPS can give me the specifications of the red metal film capacity in the top right hand corner of the board (see attached photo)? I have a damaged unit with that capacitor broken off and want to repair it.
Also what is the difference between the units that have two 4,000uF caps (the big blue ones on the right) vs. the ones that only have 1?
Thanks,
Barry
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-29 05:38 AM . Last Modified: 2024-03-13 12:47 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:38 AM . Last Modified: 2024-03-13 12:47 AM
Helloto all.yesterdaywhile I hadthe UPSon anda load of about100Wat one pointandjumped in witha bigbang, making me jumpa10Abreakerbefore theUPS.
Idisassembledit and founda diode(D21) witha while yousmoke.thestrange thing is thatnotskippedthe diodebutas if wehadputa wire betweenthe pins.
canan insect orspider thatwas wanderinginside?
here are the pictures:
on the motherboardtherewrote:LYNX2kVAMAIN BOARD
the model of theUPSis previousto the onethat is marketedtoday
ie: SUOL1000XLI
instead of the current:SURT1000XLI
wherethereis little differencein components.
SUOL1000XLI
SURT1000XLI
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:38 AM . Last Modified: 2024-03-13 12:47 AM
Wasnt an insect, components fail over time, Whats the model / Serial no of the unit?
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-29 05:38 AM . Last Modified: 2024-03-13 12:47 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:38 AM . Last Modified: 2024-03-13 12:47 AM
In fact,Ihavethis thingI noteas well. Apparently therehas beena dischargeto the radiator.
hereby replacedthe diode, I will burnthesameFuses1ampere.
The UPSandthe old model1000seriessmartSUOL1000XL
withserial number: YSD3D4110613
I wantso much to thisups, has a perfect sine waveform. imppecabileidireihere isa demonstration madeby me:
APC Smart UPS 1000VA sine wave comparating line vs. ups output - YouTube
withanexternalrelaybypass: LINE<->UPS
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:38 AM . Last Modified: 2024-03-13 12:47 AM
That model number isn't correct the serial number doesn't seem right either
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-29 05:38 AM . Last Modified: 2024-03-13 12:47 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:38 AM . Last Modified: 2024-03-13 12:47 AM
my mistake
YS0304110613
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-29 05:38 AM . Last Modified: 2024-03-13 12:46 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:38 AM . Last Modified: 2024-03-13 12:46 AM
Hi Mihai,
Can you please send me a close up of the resister burned in my UPS motherboard.Picture is attached. I tried to identify the resister from your pictures,but its not clear when i enlarge it.
Thank you
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-29 05:38 AM . Last Modified: 2024-03-13 12:46 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:38 AM . Last Modified: 2024-03-13 12:46 AM
Please, somebody has the data sheet, APC LYNX 1Kva control board????
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-29 05:38 AM . Last Modified: 2024-03-13 12:46 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 05:38 AM . Last Modified: 2024-03-13 12:46 AM
On 4/30/2014 8:36 AM, Barry said:
Hi,
I am wondering if someone with this UPS can give me the specifications of the red metal film capacity in the top right hand corner of the board (see attached photo)? I have a damaged unit with that capacitor broken off and want to repair it.
Also what is the difference between the units that have two 4,000uF caps (the big blue ones on the right) vs. the ones that only have 1?
Thanks,
Barry
10mF x 100VDC
Link copied. Please paste this link to share this article on your social media post.

