Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Smart-UPS RT 8000 XL Critical - UPS: The battery power is too low to support the load

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS RT 8000 XL Critical - UPS: The battery power is too low to support the load
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
114
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:48 AM

0 Likes
4
1389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:48 AM

Smart-UPS RT 8000 XL Critical - UPS: The battery power is too low to support the load

Hi all,

I'm troubled for a Smart-UPS RT 8000 XL

the unit worked well for about six years, and last month I done a full replacement of the batteries.

Now I'm receiving the message

"Critical - UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately."

from the UPS at about 1 minutes of intervals.

I've done the reset of the setup except the network more than one time, and also self tests and runtime calibrations without success.

I've updated the firmware but the messages still remain.

I've tryed also the non documented procedure with hyper terminal for the reset but it doesn't work, I receive only the code 27 after SHIFT Y and 0

Please, can someone help?

Thanks


Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 8000
  • smart
  • ups
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:47 AM

0 Likes
0
1390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:47 AM

Ok, I do think we need to do some type of calibration to get the UPS to recognize it has more than 0 minutes actual runtime. A runtime calibration issued via the software requires a 100% battery charge and a few other conditions met. I imagine it could also deny it because of the 0 minutes reported.

I suggest you do a manual runtime calibration. This requires at least 30% load thatdoes not fluctuate more than +/- 5 to ensure accuracy of the results. You maybe should pick a non-critical load because the UPS and load will turn off at the end.

This will also require you uninstall the management card and disconnect any serial cables from the UPS. You'll want to trip the breaker to the UPS and let it run on battery power until it turns off then let it charge back up so it can re-calculate the actual runtime.

The root cause is that 0 minutes is reported even with new batteries.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:48 AM

0 Likes
0
1390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:48 AM

Hi all,

I'm troubled for a Smart-UPS RT 8000 XL

the unit worked well for about six years, and last month I done a full replacement of the batteries.

Now I'm receiving the message

"Critical - UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately."

from the UPS at about 1 minutes of intervals.

I've done the reset of the setup except the network more than one time, and also self tests and runtime calibrations without success.

I've updated the firmware but the messages still remain.

I've tryed also the non documented procedure with hyper terminal for the reset but it doesn't work, I receive only the code 27 after SHIFT Y and 0

Please, can someone help?

Thanks


Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:48 AM

0 Likes
0
1390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:48 AM

Can you provide your event.txt, data.txt and config.ini file from your management card please? instructions are @ http://www.apc.com/site/support/index.cfm/faq/ and search for FA156131.

also, what is the load percentage on the UPS and available runtime?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:48 AM

0 Likes
0
1390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:48 AM

These are the files:

ftp://guest:guest@reguittinet.com/event.txt

ftp://guest:guest@reguittinet.com/data.txt

ftp://guest:guest@reguittinet.com/config.ini

The load is between the 25% and 50% but I have no idea about the available runtime,

The web interface is showing zero minutes and I cannot start a runtime calibration.

Thank you for your help.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:47 AM

0 Likes
0
1391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:37 AM . Last Modified: ‎2024-03-13 12:47 AM

Ok, I do think we need to do some type of calibration to get the UPS to recognize it has more than 0 minutes actual runtime. A runtime calibration issued via the software requires a 100% battery charge and a few other conditions met. I imagine it could also deny it because of the 0 minutes reported.

I suggest you do a manual runtime calibration. This requires at least 30% load thatdoes not fluctuate more than +/- 5 to ensure accuracy of the results. You maybe should pick a non-critical load because the UPS and load will turn off at the end.

This will also require you uninstall the management card and disconnect any serial cables from the UPS. You'll want to trip the breaker to the UPS and let it run on battery power until it turns off then let it charge back up so it can re-calculate the actual runtime.

The root cause is that 0 minutes is reported even with new batteries.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of