APC Shutdown: Difference Shutdown Baremetal-Server and VM-Server

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC Shutdown: Difference Shutdown Baremetal-Server and VM-Server
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
LSP
Crewman LSP
Crewman

Posted: ‎2023-11-24 04:28 AM

0 Likes
3
796
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-11-24 04:28 AM

APC Shutdown: Difference Shutdown Baremetal-Server and VM-Server

Hello everyone,

 

are baremetal servers and VMs shut down by different shutdown signals?
Do I understand correctly that VMs are shut down via the PowerChute Software which is connected to the vCenter and baremetal servers via the UPS?

So far this is my way of thinking:
The shutdown signal for baremetal servers is configured on the UPS under Configuration -> Shutdown -> Start of Shutdown -> Low Battery Duration -> 15 Minutes. For example, if the UPS has 15 minutes of battery life remaining, the baremetal servers are shut down.
For VMs, the shutdown is configured via the Powerchute interface. Set the delay for UPS on Battery to 30 minutes so that the shutdown is initiated after 30 minutes in battery mode.

 

Is my way of thinking correct?

 

 

Thanks in advance!

 

Greetings,
LSP

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2023-11-29 09:33 AM

In response to LSP
0 Likes
0
749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-11-29 09:33 AM

@LSP 

 

PowerChute VM will shutdown the VMs on each host, then vCenter server and finally the hosts. 

 

For other server you need to install PowerChute on each server. If you do not configure any events within PowerChute when the UPS reaches the low battery threshold the NMC send a signal to all configured PowerChute clients telling them the UPS has reached low battery. The PowerChute clients will then trigger the server shutdown. 

 

To see the list of configured PowerChute clients with the NMC log into the NMC and go to Configuration - PowerChute Clients. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2023-11-27 12:53 PM

0 Likes
2
765
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-11-27 12:53 PM

@LSP 

 

Both the host and bare-metal servers will require an instance of PowerChute running on them.

 

Within PowerChute you can configure a shutdown of the OS and in the case of a host OS the VMs when the UPS has run on battery for X minutes or when the UPS falls below X runtime. Also by default PowerChute will trigger the shutdown when the NMC reports the UPS has fallen below the configured low battery threshold. 

 

So, if you configure the low battery threshold to 15 minutes once the runtime falls below that number the NMC will send a signal to all configured PowerChute clients and they will trigger the shutdown. 

 

And, as mentioned above, you can configure PowerChute to trigger the shutdown after the UPS has run on battery for X minutes or when the runtime falls below X time. By utilizing all three methods you can stager the servers shutdown based on need.  By staggering the shutdown you can improve UPS on battery runtime. 

Reply

Link copied. Please paste this link to share this article on your social media post.

LSP
Crewman LSP
Crewman

Posted: ‎2023-11-28 04:28 AM

In response to BillP
0 Likes
1
754
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-11-28 04:28 AM

This means that the VMs are shut down via the PowerChute VM stored in the vCenter. However, the VM hosts servers are shut down by the UPS when the battery life is low. With the bare metal servers, I would only have to store the IP address on the NMC and the servers would be shut down by the UPS itself if the battery status was low. I don't necessarily have to configure the events in either case.

Thanks in advance!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2023-11-29 09:33 AM

In response to LSP
0 Likes
0
750
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-11-29 09:33 AM

@LSP 

 

PowerChute VM will shutdown the VMs on each host, then vCenter server and finally the hosts. 

 

For other server you need to install PowerChute on each server. If you do not configure any events within PowerChute when the UPS reaches the low battery threshold the NMC send a signal to all configured PowerChute clients telling them the UPS has reached low battery. The PowerChute clients will then trigger the server shutdown. 

 

To see the list of configured PowerChute clients with the NMC log into the NMC and go to Configuration - PowerChute Clients. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of