Posted: 2021-06-30 09:40 PM
This question was originally posted by Edgardo on APC forums on 8/12/2016
Good morning, I am writing from Argentina , I have an APC SURT7500XLI ups with a problem, it is in permanent bypass mode. review the rear connector and is correct , the electronic technician for ups will not find the solution , someone might give me information if you already had this problem with some other similar equipment ? Thank you very much. Sorry for my english
Posted: 2021-06-30 09:41 PM
This reply was originally posted by Liam on APC forums on 5/4/2017
Hello -
If the UPS will not come out of bypass there are a few possible causes:
1) The UPS has experienced a fault of some sort, which is what has caused it to go to bypass. Is the FAULT LED lit on the front panel of the UPS? If so, which LED's are lit on the battery bar graph on thr right side of the display? Can you supploy data and event logs from the NMC?
2) The UPS was mistakenly left in bypass for an extended period of time causing the batteries to drain. From the network management card interface, what are you seeing for battery voltage?
It would also be helpful to know how old the UPS and batteries are. Do you have the exact model and serial number of the UPS and Battery packs?
Thanks
Liam
Posted: 2021-06-30 09:41 PM
This was originally posted on APC forums on 5/4/2017
Hi, I am Mufeed from UAE, i also having the same issue with my two units of APC Smart UPS - SRT 8000. It is permanently on bypass mode even the terminal input supply are perfect.
Did you get any solution to rectify this issue from Schneider.? If it is sorted out please help me too.
Thanks
Posted: 2021-06-30 09:41 PM
This reply was originally posted by Edgardo on APC forums on 5/4/2017
Good morning Mufeed, APC technicians, gave me email support and asked me to do a series of tests for soft and key combination of the panel. The results are sent to them and after a couple of tests, they told me that the equipment did not have a solution and that they would buy a new UPS. At the same time I was handling the support of APC LATIN AMERICA and they did not give me a favorable answer. I hope you have better luck than me. Bye.
Posted: 2021-06-30 09:41 PM
This reply was originally posted by Liam on APC forums on 5/4/2017
Hello -
If the UPS will not come out of bypass there are a few possible causes:
1) The UPS has experienced a fault of some sort, which is what has caused it to go to bypass. Is the FAULT LED lit on the front panel of the UPS? If so, which LED's are lit on the battery bar graph on thr right side of the display? Can you supploy data and event logs from the NMC?
2) The UPS was mistakenly left in bypass for an extended period of time causing the batteries to drain. From the network management card interface, what are you seeing for battery voltage?
It would also be helpful to know how old the UPS and batteries are. Do you have the exact model and serial number of the UPS and Battery packs?
Thanks
Liam