Hi,
We have a 2 year old UPS "SMT3000RM2U" S/N: JS1052002648. We got 2 months ago the LED notifying us to change the battery. So we got a new one from APC, replaced it, after about 24 hours, made a self test and it was OK. After a week or so, the LED came back. try to do a self test, nothing, fails.
some of the info:
Dec 2010
Feb 2013
Still says Mar 2011
Any ideas?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:51 PM . Last Modified: 2024-03-11 04:26 AM
Glad to hear! ![]()
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:51 PM . Last Modified: 2024-03-11 04:26 AM
Hello.
After reviewing this, to me, it seems like a battery problem. But then the fact that it is within a normal temperature range and the predicted replacement date still says 2011, makes me think the battery isn't actually bad.
I assume it reports 100% charged? If it is, run another self test, and if it still fails, let me know. It was also suggested to look to a firmware upgrade of the UPS incase we think this is something strange with the UPS firmware considering the predicted replace battery date did not update either.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:51 PM . Last Modified: 2024-03-11 04:26 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:51 PM . Last Modified: 2024-03-11 04:26 AM
Thanks for the reply. I already tried another test and it failed again.
I will try to find a firmware updateif available
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:51 PM . Last Modified: 2024-03-11 04:26 AM
Alrighty. In our knowledge base, you can verify what the latest version is. Go to http://www.apc.com/site/support/index.cfm/faq/ and search for FA164737. you can upgrade your UPS via the Firmware Upgrade Wizard (via serial cable on your model most likely) or via a network management card. I can't tell if you're using a management card or PowerChute Business Edition. Either method requires the UPS output to turn off to do the upgrade so plan accordingly.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:51 PM . Last Modified: 2024-03-11 04:26 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:51 PM . Last Modified: 2024-03-11 04:26 AM
Hi,
Had to schedule it for the past weekend since my production switches are connected to it. Firmware updated, the error disappeared and the predicted date changed to 2017. All OK now.
Big Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:51 PM . Last Modified: 2024-03-11 04:26 AM
Glad to hear! ![]()