Posted: 2021-06-29 11:51 PM . Last Modified: 2024-03-11 04:26 AM
Hi,
I have 2 older models of APC SmartUPS 1500VA (DLA1500I). This is the apcupsd info about them:
Older one:
APC : 001,043,1053
DATE : 2013-03-20 21:38:21 +0100
HOSTNAME : szafran
VERSION : 3.14.10 (13 September 2011) debian
UPSNAME : szafran
CABLE : USB Cable
DRIVER : USB UPS Driver
UPSMODE : Stand Alone
STARTTIME: 1970-01-01 01:00:48 +0100
MODEL : Smart-UPS 1500
STATUS : ONLINE
LINEV : 226.0 Volts
LOADPCT : 4.5 Percent Load Capacity
BCHARGE : 100.0 Percent
TIMELEFT : 167.0 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME : 0 Seconds
OUTPUTV : 226.0 Volts
SENSE : High
DWAKE : -01 Seconds
DSHUTD : 090 Seconds
LOTRANS : 208.0 Volts
HITRANS : 253.0 Volts
RETPCT : 015.0 Percent
ITEMP : 32.4 C Internal
ALARMDEL : No alarm
BATTV : 27.4 Volts
LINEFREQ : 50.0 Hz
LASTXFER : No transfers since turnon
NUMXFERS : 0
TONBATT : 0 seconds
CUMONBATT: 0 seconds
XOFFBATT : N/A
SELFTEST : NO
STESTI : 14 days
STATFLAG : 0x07000008 Status Flag
MANDATE : 2008-01-25
SERIALNO : AS0804122403
BATTDATE : 2013-03-01
NOMOUTV : 230 Volts
NOMBATTV : 24.0 Volts
FIRMWARE : 653.13.I USB FW:7.3
END APC : 2013-03-20 21:38:24 +0100
Newer one:
APC : 001,043,1049
DATE : 2013-03-20 21:38:05 +0100
HOSTNAME : NAS
VERSION : 3.14.10 (13 September 2011) debian
UPSNAME : APC1500
CABLE : USB Cable
DRIVER : USB UPS Driver
UPSMODE : Stand Alone
STARTTIME: 2013-03-19 23:49:34 +0100
MODEL : Smart-UPS 1500
STATUS : ONLINE
LINEV : 226.0 Volts
LOADPCT : 16.2 Percent Load Capacity
BCHARGE : 094.0 Percent
TIMELEFT : 685.0 Minutes
MBATTCHG : 0 Percent
MINTIMEL : 0 Minutes
MAXTIME : 0 Seconds
OUTPUTV : 226.0 Volts
SENSE : High
DWAKE : -01 Seconds
DSHUTD : 090 Seconds
LOTRANS : 208.0 Volts
HITRANS : 253.0 Volts
RETPCT : 015.0 Percent
ITEMP : 25.6 C Internal
ALARMDEL : No alarm
BATTV : 26.9 Volts
LINEFREQ : 50.0 Hz
LASTXFER : No transfers since turnon
NUMXFERS : 0
TONBATT : 0 seconds
CUMONBATT: 0 seconds
XOFFBATT : N/A
SELFTEST : NO
STESTI : 14 days
STATFLAG : 0x07000008 Status Flag
MANDATE : 2009-09-16
SERIALNO : AS0938111689
BATTDATE : 2013-03-15
NOMOUTV : 230 Volts
NOMBATTV : 24.0 Volts
FIRMWARE : 653.18.I USB FW:7.4
END APC : 2013-03-20 21:38:07 +0100
In both of these the fans run at modes. The main difference is that in the older one the fan is either off or on at high rpm, in the newer one the fan is either on at low rpm or on at high rpm.
Why there is such a big difference between those two units regarding the fan control ? Is this normal ?
Is there some kind of FW update (or maybe some option I can setup in the programming mode via RS232) for the older unit to make it's fan always on but using low/high rpm as is the newer unit ?
Best regards
Szafran
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:51 PM . Last Modified: 2024-03-11 04:26 AM
I believe this was changed by design. Unfortunately, these model UPSs are not firmware upgradable in the field..there won't be much you'll be able to do yourself but I can at least say the change was made to keep the fan on low all the time in an effort to keep the UPS cooler overall in all operation modes.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:51 PM . Last Modified: 2024-03-11 04:26 AM
I believe this was changed by design. Unfortunately, these model UPSs are not firmware upgradable in the field..there won't be much you'll be able to do yourself but I can at least say the change was made to keep the fan on low all the time in an effort to keep the UPS cooler overall in all operation modes.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 11:51 PM . Last Modified: 2024-03-11 04:26 AM
I just have to make something on my own to get the older one cooled.