Hi Shampad,
There are a few steps required before HTTPS will work - specifically it needs to be enabled in the interface under "Configuration --> Network --> Web -> Access". By default the card will create a self-generated certificate, and will be configured for TLS 1.1 - depending on your environment and browser configuration you might need to change the "minimum protocol" to TLS 1.2.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0806:04 AM. Last Modified: 2024-02-1512:08 AM
Hi Shampad,
There are a few steps required before HTTPS will work - specifically it needs to be enabled in the interface under "Configuration --> Network --> Web -> Access". By default the card will create a self-generated certificate, and will be configured for TLS 1.1 - depending on your environment and browser configuration you might need to change the "minimum protocol" to TLS 1.2.