APC AP9210 Password Recovery

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC AP9210 Password Recovery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:26 PM

0 Likes
8
2343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:26 PM

APC AP9210 Password Recovery

I have recently purchased an APC AP9210 from eBay and understand that in order to retrieve my default password, I need to provide the serial number for my unit. The serial number for my unit is WA9831003175 Thank you for any help that you may be able to provide.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • ap9210
  • password
  • reset
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:25 PM

0 Likes
0
2343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:25 PM

I too have an AP-9210 for which I need to password reset.

Serial #  WA9933007316

MAC 00:C0:B7:92:6A:24

 

Thanks

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:26 PM

0 Likes
0
2343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:26 PM

Hi,

Use lower case apc for user name in either hyper-terminal or telnet (won't work via the web)

Use the following for password (any letters are capitalized) 1265<;^IBB>=

You will then have to log in again but use lower case apc for both user name and password.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:26 PM

0 Likes
0
2343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:26 PM

Thanks Bill! That certainly did do the trick! I'm curious how these units get in this state? I've done some testing by powering off the unit, resetting the unit using the menu, and holding the reset button down for 10-15 seconds and I can still log in using apc/apc. If this particular device does end up in the state that I received it in, can I just use the password that you supplied again to get access to the account apc/apc?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:26 PM

0 Likes
0
2343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:26 PM

I've taken ownership of several old remote SU5000T's, and no one remembers the passwords. We are planning to replace later in the year, but I would like to make sure these are working properly without traveling to the other side of the country. Can you help please? 

QS0607110110

QS0604111009

ZS0541007925

NA0723011813 (might be an SURT8000XLT)?

  • Tags:
  • password
  • reset
  • su5000t
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:25 PM

0 Likes
0
2343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:25 PM

Mark,

This thread is discussing password reset for AP9210 not SU5000 or SURT8000.

Those Smart-UPS do not have a default user name or password. If there are network management cards is the Smart-UPS the default user name is apc and passwords is apc. If you need assistance resetting the user name and password on the network management cards see FAQ http://www.schneider-electric.us/en/faqs/FA156075/

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:25 PM

0 Likes
0
2343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:25 PM

Bill can you please help

AP9210

WA9814798854

00 C0 B7 92 1A F2

Thanks 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:25 PM

0 Likes
0
2344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:25 PM

I too have an AP-9210 for which I need to password reset.

Serial #  WA9933007316

MAC 00:C0:B7:92:6A:24

 

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:25 PM

0 Likes
0
2343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:25 PM

Hi Rich,

Use lower case apc for user name in either hyper-terminal or telnet (won't work via the web)

Use the following for password  8;;<::^IBB<@ (any letters are capitalized)

You will then have to log in again but use lower case apc for both user name and password

 

Please note that these units are no longer supported, and we recommend taking them out of service. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:25 PM

0 Likes
0
2343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:25 PM

Hi Paul,

Use lower case apc for user name in either hyper-terminal or telnet (won't work via the web)

Use the following for password 12:76<^IBC>? (any letters are capitalized)

You will then have to log in again but use lower case apc for both user name and password

 

Please note that these units are no longer supported, and we recommend taking them out of service. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore