Self-test turns output power off

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Self-test turns output power off
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:26 PM

0 Likes
4
1860
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:26 PM

Self-test turns output power off

Hello!

We have 2 Smart-UPS 3000RM's with AP9618 management cards. Systems are set up so that every 2 weeks they make a self test. Last month one of the UPS's started to cause trouble. It initiated self-test, but then it triggers a output power off because of an overload. That UPS has load of 16.9% only. Here's the log:

14.07.201313:18:36UPS: Passed a self-test.
14.07.201313:18:21UPS: The output power is now turned on.
14.07.201313:18:21UPS: The load no longer exceeds 100% of rated capacity.
14.07.201313:18:20UPS: Started a self-test.
14.07.201312:56:12UPS: The output power is turned off due to an overload.
14.07.201312:56:09UPS: A low battery condition no longer exists.
14.07.201312:56:09UPS: The load exceeds 100% of rated capacity.
14.07.201312:56:07UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
14.07.201312:56:02UPS: Started a self-test.

The UPS won't turn on output power unless I remove 2 plugged in cords. After that I can turn UPS on, it starts and I can plug in removed cords. What might have caused this kind of problem and what can I do to fix it?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:26 PM

0 Likes
0
1860
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:26 PM

How old are the batteries in this system? It also could be a "battery overload" type situation for when the UPS is transferring to battery power during the self test. When I first read this, my first thought is an old faulty battery causing this type of behavior but I wanted to check with you on the age of this installed battery.

Also, not sure if you're able to, but do you see the same behavior if you manually transfer the UPS to battery too? (like pull the plug from the wall on the UPS or trip the upstream breaker?)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:26 PM

0 Likes
0
1861
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:26 PM

How old are the batteries in this system? It also could be a "battery overload" type situation for when the UPS is transferring to battery power during the self test. When I first read this, my first thought is an old faulty battery causing this type of behavior but I wanted to check with you on the age of this installed battery.

Also, not sure if you're able to, but do you see the same behavior if you manually transfer the UPS to battery too? (like pull the plug from the wall on the UPS or trip the upstream breaker?)

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:26 PM

0 Likes
0
1860
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:26 PM

I will test this out during weekend.

Batterys are from when we purchased UPSs. So couple years at least. But UPS itself has not yet requested new ones smile


Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:25 PM

0 Likes
0
1860
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:31 AM . Last Modified: ‎2024-03-12 11:25 PM

Yeah what I am saying this might be the UPSs way of requesting it. Depending on how the battery is failing internally (since it has chemicals, plates, etc) it might not be having an issue with voltage drop while applied with a load (which is what the self test does) but it could be failing when load is applied to it in a different way (overloading the inverter or similar).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:25 PM

0 Likes
0
1860
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:32 AM . Last Modified: ‎2024-03-12 11:25 PM

You were right! The cause is dead battery's.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore