APC AP7900: Access to the Control Console will be denied

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC AP7900: Access to the Control Console will be denied
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-14 03:51 AM

0 Likes
2
2450
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-14 03:51 AM

APC AP7900: Access to the Control Console will be denied

I just got apc ap7900 delived to my door and im sitting trying to figureout whats going on.
I followed the instructions how to connect onto it by using a serial port.
I presed a reset button on the case before starting.
Now using hyperterminal i connect to the pdu and here is what i get:
User Name : apc
Password : ***
User Name : apc
Password : ***
User Name : apc
Password : ***
Access to the Control Console will be denied for 2 minutes.

Whats next? i cant login and there is no manual to this situation.

Beforend thank you.

Message was edited by: piplite

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-14 03:51 AM

0 Likes
0
2450
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-14 03:51 AM

I wanted to post here for anyone else who comes across this thread. There are two conflicting documents concerning the AP7900 password reset/recovery procedure. [This guide|http://www.apcmedia.com/salestools/ASTE-6Z6K56_R0_EN.pdf] (page 13) contains an incomplete set of instructions; [this one|http://www.apcmedia.com/salestools/ASTE-6Z6KAM_R0_EN.pdf] contains the correct procedure.

To reset the AP7900 authentication credentials, you have to press (and hold for roughly 2 seconds) the reset button once, and then press it again once the Ethernet LEDs begin alternating quickly between green and amber. If it worked, you can then login with apc:apc.

Message was edited by: stretch

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-14 03:51 AM

0 Likes
0
2450
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-14 03:51 AM

I presume that you are using the 940-0144 (RJ-12 to DB9) cable to configure the IP Address for the Rack PDU. Please make sure that you are using the following COM port settings while you are establishing hyper terminal. 9600 bps, 8 data bits, no parity, 1 stop bit, and no flow control. Could you please let me know the Status and Link/RX/TX status lights which appear?

You can also use Address resolution protocol (ARP) to configure the rack PDU. The MAC Address of the NMC is needed for this method of configuration. The MAC address is located on the quality assurance slip that shipped with the NMC, and is also located on a white sticker on the NMC itself. From a computer on the same subnet as the unconfigured NMC, follow these instructions: The MAC Address of the inbuilt NMC of the rPDU is normally located on a white bar code sticker at the bottom.

Open up a command prompt and type the following (replacing and with actual values):

arp-s

**Mac Address format: xx-xx-xx-xx-xx-xx**

On Mac OS X: sudoarp-s

Next, use Ping with a size of 113 bytes to assign the IP address defined by the ARP command.

For the IP address defined in step 1, use one of the following Ping commands:

Windows command format: ping-l113
[To clarify, the -l option is the letter L but must be lowercase when executing the command, as noted above.]
LINUX command format: ping-s113
Mac OS X command format: ping-s113


Now, you can Telnet to the card by typing: telnet
Use "apc" for username and password.
Log out to save changes.

I hope that this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-14 03:51 AM

0 Likes
0
2451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-14 03:51 AM

I wanted to post here for anyone else who comes across this thread. There are two conflicting documents concerning the AP7900 password reset/recovery procedure. [This guide|http://www.apcmedia.com/salestools/ASTE-6Z6K56_R0_EN.pdf] (page 13) contains an incomplete set of instructions; [this one|http://www.apcmedia.com/salestools/ASTE-6Z6KAM_R0_EN.pdf] contains the correct procedure.

To reset the AP7900 authentication credentials, you have to press (and hold for roughly 2 seconds) the reset button once, and then press it again once the Ethernet LEDs begin alternating quickly between green and amber. If it worked, you can then login with apc:apc.

Message was edited by: stretch

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore