Matrix 5000 Runtime Calibration

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Matrix 5000 Runtime Calibration
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:57 PM . Last Modified: ‎2024-03-14 03:52 AM

0 Likes
7
930
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:57 PM . Last Modified: ‎2024-03-14 03:52 AM

Matrix 5000 Runtime Calibration

Hello,

Can you do a runtime calibration on a Matrix 5000 with everything still plugged in without it shutting down everything?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 10:57 PM . Last Modified: ‎2024-03-14 03:51 AM

0 Likes
0
932
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:57 PM . Last Modified: ‎2024-03-14 03:51 AM

Hi,

The calibration for the Matrix UPS must be run manually, not using any software or accessories. You can initiate the Cal Test from the front display, or if absolutely necessary, by removing input power from the unit. You can find instructions here. These must be followed to the letter, else the runtime cal. is likely to fail.

If this hasn't worked, there is either a problem with the EU, or one of the battpacks is not reporting itself to the EU. Check the status page for battery information and make sure the # of packs looks correct and the correct types are identified (XR vs. regular SmartCell). Also make sure there are no red LEDs on the batt packs. If this all looks correct, you can try reseating the EU. Unscrew the large screw in the back of the UPS that joins the top and bottom sections, and lift up, then set down the EU. Screw the separating screw back into place. This will put the UPS into bypass FYI, but is generally load-safe.

If the above steps don't fix the issue, it is likely the EU is bad. The batt packs only report three things: "I am Present", "I am good/bad", "I am Battery Type +xyz+". Therefore the battery pack would not be causing the issue unless it is just not showing up or is reporting itself as the wrong type of pack, which would be a comm card issue. The IU (bottom portion) of the UPS would not be related to this issue.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:57 PM . Last Modified: ‎2024-03-14 03:52 AM

0 Likes
0
932
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:57 PM . Last Modified: ‎2024-03-14 03:52 AM

Erin,

If you have installed the Management Software, you can initiate the run time calibration through Software on your Matrix 5000 with everything still plugged in without it shutting down everything. Please make sure that the battery is at 100% charge when the Runtime Calibration is initiated/started.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:57 PM . Last Modified: ‎2024-03-14 03:52 AM

0 Likes
0
932
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:57 PM . Last Modified: ‎2024-03-14 03:52 AM

Thanks for the reply. I did that and let the machine do the test, but now it only shows 4 min. of runtime. The load is 21%. There are 2 smartcells with this, and that is not showing the correct runtime. What could be the problem you think? These batteries were plugged in all weekend charging, they said 100% so I did the test. Don't really understand. Thanks for any help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:57 PM . Last Modified: ‎2024-03-14 03:52 AM

0 Likes
0
932
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:57 PM . Last Modified: ‎2024-03-14 03:52 AM

How old are the batteries? Have the original batteries that came with the UPS ever been replaced?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:57 PM . Last Modified: ‎2024-03-14 03:52 AM

0 Likes
0
932
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:57 PM . Last Modified: ‎2024-03-14 03:52 AM

Yes. The batteries were just replaced. I have never seen this before. Usually, when I switch the battery packs, the runtime would shoot up. But this time it did not. Do you think it could be an EU fault? It shows it has 2 battery packs. I also did not get the message that battery packs have changed. Is there a way to dead brain this unit, maybe that will reset something? Just throwing ideas out there. Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:57 PM . Last Modified: ‎2024-03-14 03:51 AM

0 Likes
0
932
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:57 PM . Last Modified: ‎2024-03-14 03:51 AM

Did you replace the SmartCell batteries with third party batteries? May I know the version of the Power Chute software which is being used?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:57 PM . Last Modified: ‎2024-03-14 03:51 AM

0 Likes
0
932
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:57 PM . Last Modified: ‎2024-03-14 03:51 AM

No, I am a partner with APC, and I replaced the batteries with APC batteries. There is no powerchute with this machine. This machine was given to the company when they moved in. The original batteries were hot to the touch, so I replaced them.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 10:57 PM . Last Modified: ‎2024-03-14 03:51 AM

0 Likes
0
933
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:57 PM . Last Modified: ‎2024-03-14 03:51 AM

Hi,

The calibration for the Matrix UPS must be run manually, not using any software or accessories. You can initiate the Cal Test from the front display, or if absolutely necessary, by removing input power from the unit. You can find instructions here. These must be followed to the letter, else the runtime cal. is likely to fail.

If this hasn't worked, there is either a problem with the EU, or one of the battpacks is not reporting itself to the EU. Check the status page for battery information and make sure the # of packs looks correct and the correct types are identified (XR vs. regular SmartCell). Also make sure there are no red LEDs on the batt packs. If this all looks correct, you can try reseating the EU. Unscrew the large screw in the back of the UPS that joins the top and bottom sections, and lift up, then set down the EU. Screw the separating screw back into place. This will put the UPS into bypass FYI, but is generally load-safe.

If the above steps don't fix the issue, it is likely the EU is bad. The batt packs only report three things: "I am Present", "I am good/bad", "I am Battery Type +xyz+". Therefore the battery pack would not be causing the issue unless it is just not showing up or is reporting itself as the wrong type of pack, which would be a comm card issue. The IU (bottom portion) of the UPS would not be related to this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of