Hi,
Is there any software to monitor an APC 2200 that doesn't have a Network Management Card but has a serial port? I currently have a server connected to the UPS via a serial cable. I was wondering if there was something I could install on the server to monitor the UPS.
Anything?
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:06 AM . Last Modified: 2024-03-13 03:17 AM
you can use powerchute plus if it is supported on your OS but the software is old and we can only support it to a certain extent because of that.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:06 AM . Last Modified: 2024-03-13 03:17 AM
hi..yes, you'd need to look at PowerChute Business Edition. you can start here and chose Software Upgrades - PowerChute Business Edition and then select submit. It will ask you to choose the software for your OS. If you only have this one device, I recommend just installing the "Agent" portion which you can access afterwards via a web browser on the client or remotely from another machine via IP.
this gives you monitoring capability, email, and graceful shutdown.
hope that helps.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:06 AM . Last Modified: 2024-03-13 03:17 AM
Use Powerchute Plus It's a lot better than PCBE
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:06 AM . Last Modified: 2024-03-13 03:17 AM
you can use powerchute plus if it is supported on your OS but the software is old and we can only support it to a certain extent because of that.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.