APC 10KA After resetting NMC Card default username and password not working

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC 10KA After resetting NMC Card default username and password not working
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
MohamadSami
MohamadSami
Cadet

Posted: ‎2024-07-04 12:46 AM

0 Likes
4
1707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-04 12:46 AM

APC 10KA After resetting NMC Card default username and password not working

I have an APC 10KA Model SRT10KXLI connected to the internet and set the IP Address.

I have reached the web interface and inserted the typical Username and password:

apc

apc

 

But it did not work, I tried multiple ones

apcuser

apc

 

admin

admin

 etc...

I gave up and resetted the NMC card using a toothpick. The NMC got resetted, trying again with

apc

apc

 

it did not work

 

Tried with multiple password and username combination....ALL not working.

 

i am Baffled and have no idea what do ?

 

I tried reading the manual, read the guide etc... read many things, nothing to be found.
I thought maybe the username and password to be found in the device, but couldnt find it anywhere.

 

Can someone please help me?

  • Tags:
  • setting username & pswrd in web portal se according to the guide will enter whether it is uppercase or lowercase
  • thanks.
  • the length of the character or symbol. now i need IP Address of NMC because error registering
  • where we know IP Address of NMC... my Error is P11
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
MorneMeintjes
Ensign MorneMeintjes
Ensign

Posted: ‎2024-07-04 11:57 PM

0 Likes
2
1673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-04 11:57 PM

Good Morning

 

for the older NMC I have used the following.

 

Depress the NMC Reset button using a paper clip or some similar device. When
the card begins to reboot depress the Reset button again. As soon as the NMC
has completed rebooting, log in using apc/apc for the user name/password.
Note: You must log in within thirty seconds of the NMC reboot, otherwise,
repeat the process.

 

I hope this helps

Best Regards

Reply

Link copied. Please paste this link to share this article on your social media post.

MohamadSami
MohamadSami
Cadet

Posted: ‎2024-07-08 10:24 PM

In response to MorneMeintjes
0 Likes
1
1622
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-08 10:24 PM

Hello MorneMeintjes,

 

I tried your method, I even timed it to 10 seconds.

But the method still did not work, still gives me Invalid username and password and try again.

Any more ideas?

Reply

Link copied. Please paste this link to share this article on your social media post.

MorneMeintjes
Ensign MorneMeintjes
Ensign

Posted: ‎2024-07-10 12:54 AM

In response to MohamadSami
0 Likes
0
1597
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-10 12:54 AM

Morning

Unfortunately not.

have you requested help from SE's CCC, Please find their email be,ow

esupport.africaen@schneider-electric.com

 

Hope you find a solution.

Best Regards

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-07-10 05:47 AM . Last Modified: ‎2024-07-10 05:47 AM

0 Likes
0
1588
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-10 05:47 AM . Last Modified: ‎2024-07-10 05:47 AM

Format the NMC as outlined in the user manual / FAQ. Once the NMC has been properly formatted the default user name / password is all lower case: apc 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore