AP9631 detbat -all E101 Command Not Found
UPS Smart RT 6000 XL
An input power failure has occurred. After power is restored UPS is showing errors. apc>detstatus -all E000: Success Status of UPS: Internal Fault Bypass, Inverter Fault, No Other Alarms Present Last Transfer: No transfers have occurred Runtime Remaining: 1 hr 17 min Battery State Of Charge: 23.0 % Output Voltage: 237.6 VAC Output Frequency: 50.0 Hz Output Watts Percent: 16.0 % Output VA Percent: 10.0 % Output Current: 2.56 A Input Voltage: 237.6 VAC Input Frequency: 50.0 Hz Battery Voltage: 192.2 VDC Internal Temperature: 25.7 C, 78.2 F Self-Test Result: Invalid Self-Test Date: 07/09/2024 Calibration Result: Not Available Calibration Date: Unknown
Batteries are 7 - years old. The batteries are not being charged after power is restored
Schneider Electric Network Management Card AOS v7.1.2 (c) Copyright 2023 All Rights Reserved Smart-UPS & Matrix-UPS APP v7.1.2 ------------------------------------------------------------------------------- Name : apc9BDCD7 Date : 07/10/2024 Contact : Unknown Time : 08:02:16 Location : Unknown User : Super User Up Time : 0 Days 11 Hours 16 Minutes Stat : P+ N+ A+ -------------------------------------------------------------------------------