Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-09 11:02 PM . Last Modified: 2024-07-09 11:08 PM
UPS Smart RT 6000 XL
An input power failure has occurred. After power is restored UPS is showing errors.
apc>detstatus -all
E000: Success
Status of UPS: Internal Fault Bypass, Inverter Fault, No Other Alarms Present
Last Transfer: No transfers have occurred
Runtime Remaining: 1 hr 17 min
Battery State Of Charge: 23.0 %
Output Voltage: 237.6 VAC
Output Frequency: 50.0 Hz
Output Watts Percent: 16.0 %
Output VA Percent: 10.0 %
Output Current: 2.56 A
Input Voltage: 237.6 VAC
Input Frequency: 50.0 Hz
Battery Voltage: 192.2 VDC
Internal Temperature: 25.7 C, 78.2 F
Self-Test Result: Invalid
Self-Test Date: 07/09/2024
Calibration Result: Not Available
Calibration Date: Unknown
Batteries are 7 - years old. The batteries are not being charged after power is restored
Schneider Electric Network Management Card AOS v7.1.2
(c) Copyright 2023 All Rights Reserved Smart-UPS & Matrix-UPS APP v7.1.2
-------------------------------------------------------------------------------
Name : apc9BDCD7 Date : 07/10/2024
Contact : Unknown Time : 08:02:16
Location : Unknown User : Super User
Up Time : 0 Days 11 Hours 16 Minutes Stat : P+ N+ A+
-------------------------------------------------------------------------------
apc>detbat -all
E101: Command Not Found
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-10 04:35 AM
Based on the active faults / error log you have a couple of serious problems. Primarily an inverter fault, followed by a bypass fault.
Given the batteries are seven years old they are well past their expected service life of 3-5 years.
I would start by replacing the battery cartridges, reset the unit. Power up the unit to see if the inverter fault clears which I highly doubt.