AP9921X Battery Monitoring System

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9921X Battery Monitoring System
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 06:05 AM . Last Modified: ‎2024-02-15 12:08 AM

0 Likes
8
1018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:05 AM . Last Modified: ‎2024-02-15 12:08 AM

AP9921X Battery Monitoring System

I have recently installed an AP9921X Battery Monitoring unit in an existing system. I am able to get the battery voltage readings, but I am getting "Ohmic Data Not Available" when trying to look that data up. When programming this unit is there a line or box I may have missed to allow the unit to take the ohmic readings?

I appreciate all the help.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 06:05 AM . Last Modified: ‎2024-02-15 12:08 AM

0 Likes
0
1018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:05 AM . Last Modified: ‎2024-02-15 12:08 AM

I understand the proprietary aspect of the system. The discharge and the full charge of the batteries after is the signal to the BMS that the battery string is good?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
B-DoubleE_apc
Commander B-DoubleE_apc
Commander

Posted: ‎2021-07-08 06:05 AM . Last Modified: ‎2024-02-15 12:08 AM

0 Likes
0
1018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:05 AM . Last Modified: ‎2024-02-15 12:08 AM

Hi James,

Ohmic values are only generated when the BMS considers all batteries on a particular string fully charged, and has been placed under a discharge with at least a 50 amp load

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 06:05 AM . Last Modified: ‎2024-02-15 12:08 AM

0 Likes
0
1019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:05 AM . Last Modified: ‎2024-02-15 12:08 AM

Just checking for understanding, I will not be able to see ohmic values until there has been a discharge of least a 50 amp load? Is there only time the ohmic values available after a discharge? Maybe I should change ohmic with resistance readings. As this system is right now my network personnel can see the voltages, but not the resistance of the batteries in this system. I am sure I probably missed something while programming in the battery string information on this BMS.

Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

B-DoubleE_apc
Commander B-DoubleE_apc
Commander

Posted: ‎2021-07-08 06:05 AM . Last Modified: ‎2024-02-15 12:08 AM

0 Likes
0
1019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:05 AM . Last Modified: ‎2024-02-15 12:08 AM

Technically it requires a discharge of "20% of battery percentage after battery voltages were polled" - the complete list of what the BMS requires to generate ohmic values can be found here: https://www.apc.com/us/en/faqs/FA156171/

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 06:05 AM . Last Modified: ‎2024-02-15 12:08 AM

0 Likes
0
1018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:05 AM . Last Modified: ‎2024-02-15 12:08 AM

This is information useful. Is this the same situation when batteries are replaced? Will, they need to be discharged after the batteries are fully charged to be able to see the resistance values of the new batteries? 

Reply

Link copied. Please paste this link to share this article on your social media post.

B-DoubleE_apc
Commander B-DoubleE_apc
Commander

Posted: ‎2021-07-08 06:05 AM . Last Modified: ‎2024-02-15 12:08 AM

0 Likes
0
1018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:05 AM . Last Modified: ‎2024-02-15 12:08 AM

That's correct - the ohmic values are timestamped with the date of the discharge event. If the batteries are replaced, a new discharge event would need to occur before new values are shown.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 06:05 AM . Last Modified: ‎2024-02-15 12:08 AM

0 Likes
0
1018
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:05 AM . Last Modified: ‎2024-02-15 12:08 AM

I will need to pass this information on. How does the BMS update the resistance values we are able to see as the batteries age? I would not think it would have to wait until another discharge. I would believe the BMS is set up to do a "battery check" at a predetermined time frame and will give the updated resistance so that a battery can be replaced before it goes bad and if a discharge is needed not having battery availability.

I do appreciate the time you are giving me as I know how busy we all are.

Reply

Link copied. Please paste this link to share this article on your social media post.

B-DoubleE_apc
Commander B-DoubleE_apc
Commander

Posted: ‎2021-07-08 06:05 AM . Last Modified: ‎2024-02-15 12:08 AM

0 Likes
0
1019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:05 AM . Last Modified: ‎2024-02-15 12:08 AM

When the BMS senses a battery string is good, it runs a "benchmark" test (the nature of the test is considered proprietary) to get most values. Every 6.5-7 hours the benchmark test is repeated

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 06:05 AM . Last Modified: ‎2024-02-15 12:08 AM

0 Likes
0
1019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 06:05 AM . Last Modified: ‎2024-02-15 12:08 AM

I understand the proprietary aspect of the system. The discharge and the full charge of the batteries after is the signal to the BMS that the battery string is good?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of