AP9631 not upgradeable and now unuseable

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9631 not upgradeable and now unuseable
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 01:18 AM . Last Modified: ‎2024-02-29 10:39 PM

0 Likes
4
2242
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:18 AM . Last Modified: ‎2024-02-29 10:39 PM

AP9631 not upgradeable and now unuseable

Upgrade failed with ERROR --> Boot Monitor transfer failed.

Now it has replaced Application Module with bootmon and didn't work anymore.

Hardware Factory
---------------
Model Number:         AP9631
Serial Number:         5A1250T08561
Hardware Revision:     05
Manufacture Date:     12/15/2012
MAC Address:         00 C0 B7 9D 9E 8B
Management Uptime:     0 Days 0 Hours 1 Minute

Application Module
---------------
Name:             bootmon
Version:         v1.0.8
Date:             Apr  8 2014
Time:             10:59:40

APC OS(AOS)
---------------
Name:             aos
Version:         v5.1.7
Date:             Nov 22 2011
Time:             09:53:57

APC Boot Monitor
---------------
Name:             bootmon
Version:         v1.0.2
Date:             Jan 21 2010
Time:             13:35:57

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • error
  • NMC
  • upgrade
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:39 PM

0 Likes
0
2240
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:39 PM

Yes, I recommend trying this upgrade via BootMonitor mode to resolve. Do bootmonitor .bin file first, then AOS bin file, and then the application .bin file (whatever it may be - sumx, sy, etc). The instruction details Terry linked should be helpful for via BootMonitor/XMODEM on NMC2.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-08 01:18 AM . Last Modified: ‎2024-02-29 10:39 PM

0 Likes
0
2241
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:18 AM . Last Modified: ‎2024-02-29 10:39 PM

The directory where you unpacked the firmware update should contain 3 .bin files - the bootmon, aos, and app (which will have different names depending on what device the firmware is intended for).

FTP to the card, make sure you're in binary mode, and do a "put" of the bootmon file. Disconnect and the NMC should reboot. After it reboots, FTP to it again, also in binary mode, and "put" the aos file. Disconnect and wait for the reboot. Repeat with the app file.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:18 AM . Last Modified: ‎2024-02-29 10:39 PM

0 Likes
0
2240
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:18 AM . Last Modified: ‎2024-02-29 10:39 PM

That's what I tried beside windows update tool, too.

It doesn't matter which file I use. I get round about 20 hashes (every time the exactly same length) and after a few minutes I get a timeout and the NMC is rebooting.

I have read about AP9630 and that there was a charge which could not be updated. Wrong flash bit set or something else?

I sill formated the NMC and tried to update manually with linux and ftp on console. bin and passive or active.

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-08 01:18 AM . Last Modified: ‎2024-02-29 10:39 PM

0 Likes
0
2241
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:18 AM . Last Modified: ‎2024-02-29 10:39 PM

The upgrade issue was for cards produced for a few weeks in 2010. Yours seems to be from late 2012.

You could try one of the other upgrade methods (USB or serial XMODEM) mentioned in FA156047. Note that that article is a generic one for 3 generations of NMC. Make sure you are following the instructions for the AP9630/1.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:39 PM

0 Likes
0
2241
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:39 PM

Yes, I recommend trying this upgrade via BootMonitor mode to resolve. Do bootmonitor .bin file first, then AOS bin file, and then the application .bin file (whatever it may be - sumx, sy, etc). The instruction details Terry linked should be helpful for via BootMonitor/XMODEM on NMC2.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore