AP9631 and Gmail/Google Apps

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
wsipdx_apc
Cadet
0 Likes
37
1090

AP9631 and Gmail/Google Apps

This was originally posted on APC forums on 11/23/2011


I am having issues setting up an AP9631 using a Gmail/Google Apps account. I have the latest firmware on the 9631 (5.1.6) but I just keep getting the following error:

"Test e-mail failed; SMTP configuration error."

Any hints or tips on getting email notifications running using a Gmail hosted email account?

Thanks.


Accepted Solutions
f1ydave_apc
Crewman
Crewman
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This was originally posted on APC forums on 2/18/2015


To use SIMPLE SMTP  with GOOGLE

SMTP: gmail-smtp-in.l.google.com

No login/password required for your account. It will send the email out.

You are all welcome.

See Answer In Context

37 Replies 37
BillP
Administrator Administrator
Administrator
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This reply was originally posted by Marko on APC forums on 8/24/2013


Hi Angela,

I tried to find new fw for AP9630 but couldnt finf it.

Could You please send me new and tell how to setup gmail notification?

Best Regards,

Marko Markovic

BillP
Administrator Administrator
Administrator
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This reply was originally posted by Angela on APC forums on 8/26/2013


Start at http://www.apc.com/tools/download/index.cfm and choose Firmware Upgrades - All. For a Smart UPS, choose part number SFSUMX606 or if it is a symmetra single phase, choose SFSY606.

For setting up GMail, refer to this article -> http://www.apc.com/support/index?page=content&country=US〈=en&id=FA164769

BillP
Administrator Administrator
Administrator
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This reply was originally posted by Angela on APC forums on 5/24/2013


Should be on the website early next week or even this weekend!

BillP
Administrator Administrator
Administrator
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This reply was originally posted by Angela on APC forums on 5/28/2013


It's available!!

wsipdx_apc
Cadet
0 Likes
0
1092

AP9631 and Gmail/Google Apps

This was originally posted on APC forums on 11/23/2011


I am having issues setting up an AP9631 using a Gmail/Google Apps account. I have the latest firmware on the 9631 (5.1.6) but I just keep getting the following error:

"Test e-mail failed; SMTP configuration error."

Any hints or tips on getting email notifications running using a Gmail hosted email account?

Thanks.

robotvoice_apc
Ensign
Ensign
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This was originally posted on APC forums on 6/4/2013


I am on the latest revision of the NMC2 (v6.0.6) and I am still having trouble setting up email notifications with my gmail account.

BillP
Administrator Administrator
Administrator
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This reply was originally posted by Angela on APC forums on 6/4/2013


You can start a new thread if you want and download your config.ini and post it on the thread. Also, do you have your "last email test result" please?

jonathan789_apc
Cadet
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This was originally posted on APC forums on 6/6/2013


I've been following this thread with interest and am pleased there is an update.

I downloaded this file:-

UPS Network Management Card v6.0.6 Firmware for Smart-UPS & Galaxy 3500 with AP9630/31SFSUMX606

04/19/2013

but its not suitable?

APC support site is complex and hard to get a simple download of which firmware update we need for this product.   Can't we just enter a serial number and get all relevant updates like Dell does?

I have 2 APC Smart-UPS RT 6000 XL units I'd like to upgrade as we have Googlemail and I need to get alert this way.

Gmail requires authentication with a tick box and an mail address and password for this which the cards in this units don't support.

We will be buying another UPS system later this year, and whichever vendor we choose needs to support Googlemail for our error logs.   Lots of people have ditched their Exchange servers, so I am surprised its been slow for an update for clients like us.

BillP
Administrator Administrator
Administrator
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This reply was originally posted by Angela on APC forums on 6/6/2013


well can you verify what model of network management card you have in your Smart UPS RT 6000? If it is an AP9617/18/19 (which you can verify in the Web UI->Administration->General->About), the update will not work because its only for AP9630/31 models that are the currently manufactured management cards. AP9617/18/19 older cards have been discontinued since 2009ish now so they are no longer being given firmware updates. You'll need AP9630/31 to take advantage of this update.

Lastly, it is possible to get some Gmail functionality either older or newer cards on older firmware by going to the knowledge base (http://www.apc.com/site/support/index.cfm/faq/ )and reviewing article ID FA164769.

ptr727_apc
Ensign
Ensign
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This was originally posted on APC forums on 5/14/2013


Hi, any update on a release date?

BillP
Administrator Administrator
Administrator
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This reply was originally posted by Angela on APC forums on 5/14/2013


It should be on the website within a week or two so no documentation is public.

Before upgrading, please review http://www.apc.com/site/support/index.cfm/faq/index.cfm and look for article ID FA167693.

If you can tell me what application you're using - sumx or sy, I can send it to you privately.

ptr727_apc
Ensign
Ensign
0 Likes
0
1091

Re: AP9631 and Gmail/Google Apps

This was originally posted on APC forums on 5/14/2013


Thanks for update.

I don't understand what you mean by "symx or sy", my AP9631 came with the latest firmware already installed?

BillP
Administrator Administrator
Administrator
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This reply was originally posted by Angela on APC forums on 5/14/2013


When you go to the web interface, go to Administration->general->About and tell me what you see under Application module - you'll see something that says sumx or sy.

1155_%245CE367EEBAEEE87E.jpg

ptr727_apc
Ensign
Ensign
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This was originally posted on APC forums on 5/14/2013


Ah, ok, sumx.

BillP
Administrator Administrator
Administrator
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This reply was originally posted by Angela on APC forums on 5/14/2013


OK - I will send you a message with where to get the sumx file but keep in mind my disclaimer about no documentation available besides the kbase I provided smile

ptr727_apc
Ensign
Ensign
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This was originally posted on APC forums on 5/14/2013


Email is working smile

It took me a minute to figure out how to restore deg C to deg F, but found it under user preferences.

BillP
Administrator Administrator
Administrator
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This reply was originally posted by Angela on APC forums on 5/15/2013


Glad to hear! And yes, now each user can have their own preferences such as units of temperature.

BillP
Administrator Administrator
Administrator
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This reply was originally posted by Angela on APC forums on 11/30/2011


unfortunately i dont think this will work until or next major firmware revision. google requires SSL SMTP authentication as far as I know and we don't support that currently, only basic authentication. if this were to work, you'd need to make sure you are using recipient's mail setting (versus local). you could also try relaying the NMC email to an internal, local server, and having that send it to gmail.

i have tested gmail on an early copy of new firmware, due sometime next year, and have gotten gmail to work without issue.

jbowkett_apc
Cadet
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This was originally posted on APC forums on 1/17/2012


Do you have any idea which version this feature might be released in?....Do we need to wait for a major version upgrade to v4.x or will it be in the next minor release?...or indeed, is it in the current firmware?

BillP
Administrator Administrator
Administrator
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This reply was originally posted by Angela on APC forums on 1/17/2012


6.x which would be around later this year for the sumx, sy, and sy3p apps. probably for rpdu2g as well.

jrbereza_apc
Cadet
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This was originally posted on APC forums on 7/24/2013


I had the same problem until I used port 587 in the Email Recipient settings, then things started working properly.

far_apc
Cadet
0 Likes
0
1091

Re: AP9631 and Gmail/Google Apps

This was originally posted on APC forums on 5/22/2012


Any update on the SSL SMTP release.

Is there an ETA for this or have I missed something in 5.1.7?

BillP
Administrator Administrator
Administrator
0 Likes
0
1091

Re: AP9631 and Gmail/Google Apps

This reply was originally posted by Gene on APC forums on 2/17/2013


I do not see the 6.x release on the APC website. ( http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP9631&tab=software )

BillP
Administrator Administrator
Administrator
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This reply was originally posted by Angela on APC forums on 2/18/2013


well as you probably know, schedules change and things come up unfortunately.. we are looking at first week in March 2013 as it stands now.

BillP
Administrator Administrator
Administrator
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This reply was originally posted by Angela on APC forums on 3/12/2013


sorry - we are at March 19th as of today for release. it might be on the website a few days after that. for any emergency issues though, I can try to post it here when I get it.

SJacobson_apc
Cadet
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This was originally posted on APC forums on 10/5/2012


I have a smart UPS 700 serial. We just switched to Gmail Apps for Education and lost the email alert feature. If your not planning to fix this would you be able to provide me with models that do have the ability to work with the Gmail system? I will update our purchasing and plan to replace some with models that work.

BillP
Administrator Administrator
Administrator
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This reply was originally posted by Angela on APC forums on 10/9/2012


assuming your UPS is an SU700 or SU700NET for the exact model, AP9630 or AP9631 network management cards will be required for each UPS and our next firmware revision 6.x will work fine with gmail.

BillP
Administrator Administrator
Administrator
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This reply was originally posted by Gene on APC forums on 10/9/2012


Is there an ETA for the 6.x release that supports gmail?

BillP
Administrator Administrator
Administrator
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This reply was originally posted by Angela on APC forums on 10/9/2012


if you are using the sumx or sy app - which is for Smart UPS products and Symmetra single phase, I will most likely be able to post the firmware hopefully in December if nothing changes where it will not be on the website until later in January.

jbowkett_apc
Cadet
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This was originally posted on APC forums on 7/17/2012


@i picKed a winna, @Angela
Any update on the availability of this? This is the only thing keeping our mx records for one domain hosted with a non-secure email provider, so we would like to update as soon as possible. Is there any way we can install a patch to provide this functionality to our 3000 XLI UPS?

BillP
Administrator Administrator
Administrator
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This reply was originally posted by Angela on APC forums on 7/17/2012


sorry for the delay. for the sumx application and the new 6.x interface, we are looking at December as it stands today 😞 there is no way to provide a patch to the system unfortunately, it'd require a firmware update.

voidstar_apc
Janeway
Janeway
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This was originally posted on APC forums on 7/17/2012


You could temporarily run a SMTP server (perhaps [one of these|http://stackoverflow.com/questions/30076/need-a-lightweight-free-windows-smtp-server]) to relay mail to the gmail account, and lock it down so only the NMC has access to it.

waibel_apc
Cadet
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This was originally posted on APC forums on 8/7/2012


Any chance you could provide a link to that new firmware? 🙂

BillP
Administrator Administrator
Administrator
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This reply was originally posted by Angela on APC forums on 8/8/2012


its not done yet 🙂

ptr727_apc
Ensign
Ensign
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This was originally posted on APC forums on 4/1/2013


Hi, any update on a release date?

BillP
Administrator Administrator
Administrator
0 Likes
0
1092

Re: AP9631 and Gmail/Google Apps

This reply was originally posted by Angela on APC forums on 4/1/2013


I keep saying one thing yet it moves out so I apologize. Third week in April is what I have now. I also had put together article FA164769 in the knowledge base to try and give users the best chance of GMail and other services to work depending on what ports are open on your network or from your ISP.

f1ydave_apc
Crewman
Crewman
0 Likes
0
1093

Re: AP9631 and Gmail/Google Apps

This was originally posted on APC forums on 2/18/2015


To use SIMPLE SMTP  with GOOGLE

SMTP: gmail-smtp-in.l.google.com

No login/password required for your account. It will send the email out.

You are all welcome.