AP9631 NMC2 w/ SY656 firmware does not provide useful fault location descriptions

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9631 NMC2 w/ SY656 firmware does not provide useful fault location descriptions
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-08 05:32 AM . Last Modified: ‎2024-02-15 12:14 AM

0 Likes
2
1885
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:32 AM . Last Modified: ‎2024-02-15 12:14 AM

AP9631 NMC2 w/ SY656 firmware does not provide useful fault location descriptions

The AP9631 (and presumably the other cards in the NMC2 family) running the SY656 firmware don't provide useful fault location information when faults occur. As an example (from Status / UPS / Battery):

8lnXzYxcM1taNfheyy9Y6Q%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg8lnXzYxcM1taNfheyy9Y6Q%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg

Note that the faulted batteries are shown as Battery 1, Battery 2, and Battery 4. The XR frame has 4 positions labeled L1, R1, L2, R2. The UPS front panel fault messages correctly identify the actual position.

Status / UPS / Power does make location information available for power modules, if you know the secret of clicking on the "NA" serial number. You'll then get "Location in frame: L1" (for example).

I suggest always reporting the location of power modules and battery modules with their physical location (L1-L4 and R2-R4 for the main SYH6K6RM chassis - the MIM and RIM are where the R1 slot would be) and L1-L2 and R1-R2 for the SYRMXR4. Obviously, the slot locations vary depending on the model of Symmetra.

By the way, I seem to remember this working correctly on the AP961x NMC.

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-08 05:33 AM . Last Modified: ‎2024-02-15 12:14 AM

0 Likes
0
1885
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:33 AM . Last Modified: ‎2024-02-15 12:14 AM

It may be that the old NMC just logged the location in the event log (the front panel displays the failed location, so the UPS definitely knows which one it is).

BTW, it appears that these new batteries were not faulty - I swapped the 4 in the first XR chassis with the ones in the second XR chassis, waited for 100% charge, and did a runtime calibration again. The unit discharged to the same point, but this time reported "calibration failed" in the NMC2 event log, "Not available on August 23, 2018" in the Test / UPS menu, and "Calibration Stopped" in the front panel event log. See my other post here about that.

Here's the graph showing the calibration progress (the deep "V's" on Wed and Thu are the 2 calibrations, the first that triggered the bogus battery faults and the second that just cancelled itself for no reason):

Hd61CQ0zfznxrZz5niRfww%3D%3D.pngHd61CQ0zfznxrZz5niRfww%3D%3D.png

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:33 AM . Last Modified: ‎2024-02-15 12:14 AM

0 Likes
0
1885
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:33 AM . Last Modified: ‎2024-02-15 12:14 AM

Hi Terry,

We will see what we can do about this moving forward for a future release. The only thing though is that I don't see this being any different on the NMC1 models - AP961x as you said. I see this below:

%2BG93HKht6KlEYcC3Xf3XOQ%3D%3D.png%2BG93HKht6KlEYcC3Xf3XOQ%3D%3D.png

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-08 05:33 AM . Last Modified: ‎2024-02-15 12:14 AM

0 Likes
0
1886
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:33 AM . Last Modified: ‎2024-02-15 12:14 AM

It may be that the old NMC just logged the location in the event log (the front panel displays the failed location, so the UPS definitely knows which one it is).

BTW, it appears that these new batteries were not faulty - I swapped the 4 in the first XR chassis with the ones in the second XR chassis, waited for 100% charge, and did a runtime calibration again. The unit discharged to the same point, but this time reported "calibration failed" in the NMC2 event log, "Not available on August 23, 2018" in the Test / UPS menu, and "Calibration Stopped" in the front panel event log. See my other post here about that.

Here's the graph showing the calibration progress (the deep "V's" on Wed and Thu are the 2 calibrations, the first that triggered the bogus battery faults and the second that just cancelled itself for no reason):

Hd61CQ0zfznxrZz5niRfww%3D%3D.pngHd61CQ0zfznxrZz5niRfww%3D%3D.png

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of