hello;
we would like to pull the Temp from the sensor,
whats the OID for these cards?
AP9631/AP9619
thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:16 AM . Last Modified: 2024-03-11 02:45 AM
great thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:16 AM . Last Modified: 2024-03-11 02:45 AM
assuming you mean ambient temperature..
AP9631: .iso.org.dod.internet.private.enterprises.apc.products.hardware.universalInputOutput.uioSensor.uioSensorStatusTable.uioSensorStatusEntry / .1.3.6.1.4.1.318.1.1.25.1.2.1
take a look under that subtree for what you might need - you'll see an OID for F and C readings in addition to other sensor related items like sensor name, etc:
.1.3.6.1.4.1.318.1.1.25.1.2.1.5 - temp in F
.1.3.6.1.4.1.318.1.1.25.1.2.1.6 - temp in C
AP9619: .iso.org.dod.internet.private.enterprises.apc.products.hardware.environmentalMonitor.integrated.iemStatus.iemStatusProbesTable.iemStatusProbesEntry / .1.3.6.1.4.1.318.1.1.10.2.3.2.1 is the main subtree to check for this card
.1.3.6.1.4.1.318.1.1.10.2.3.2.1.4 - temp in your current temp preference
.1.3.6.1.4.1.318.1.1.10.2.3.2.1.5 - OID that tells you the current temp preference
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 01:16 AM . Last Modified: 2024-03-11 02:45 AM
great thanks.