Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

404 and silence alarm

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • 404 and silence alarm
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 01:15 AM . Last Modified: β€Ž2024-03-11 02:45 AM

0 Likes
5
1668
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 01:15 AM . Last Modified: β€Ž2024-03-11 02:45 AM

404 and silence alarm

Hi

I just installed a new Smart UPS 1500.
Connected to a DELL workstation.
Running Windows 7 x64 SP1.

Installed PowerChute Business Edition 9.01.
Installed Agent, installed Server, installed Console, all on same machine.

Want to configure SMTP notification.
Now way to enable SSL/TLS or configure port number.

Logged into console.
Pretty ugly UI, does not allow resizing of window, must come from the days when skinning UI's were the cool thing to do.

I get two warning messages; I need to configure the outlet grouping, and I need to configure the shutdown sequence.
Ok, I go to that section, and I get 404 error pages in the embedded IE window.

I open the agent directly using Chrome, and I get a warning that the certificate is not trusted, continue anyway.
Now I can configure shutdown sequence and outlet grouping.

Is it the bad SSL certs that is preventing the console from letting me configure?
If so, really bad first experience.

Want to register UPS.
How do I see and copy-n-paste the serial number of the UPS?
Console shows me the serial number, but it is read only, no copy.
Agent web console does not show any UPS details.

Want to run runtime calibration.
Start test, UPS starts beeping.
Where do I remotely silence the alarm, can't find any place to silence the alarm?
Have to walk to UPS to silence it.

I see there is an announcement for new Beta software, I sure hope the software usability is updated.

Ok, enough complaining.

How do I configure SSL/TLS and SMTP port number to use?
How do I access the agent configuration and not get 404 pages?
How do I get details of the hardware in a form I can copy-n-paste?
How do I remotely silence the alarm?

P.

Message was edited by: ptr727

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 01:16 AM . Last Modified: β€Ž2024-03-11 02:45 AM

0 Likes
0
1668
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 01:16 AM . Last Modified: β€Ž2024-03-11 02:45 AM

there are also other firmware upgrade options available that do not require windows, outlined here-> http://nam-en.apc.com/app/answers/detail/a_id/768

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 01:15 AM . Last Modified: β€Ž2024-03-11 02:45 AM

0 Likes
0
1668
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 01:15 AM . Last Modified: β€Ž2024-03-11 02:45 AM

hello,

I mainly stick with the agent and that is what i will try to help with. the console portion of the software is going away eventually and we will be sticking with just the agent portion via the web browser.

1.) PCBE does not currently support SSL/TLS email authentication or changing the port number - don't shoot the messenger. Both are on the roadmap for a furture release as far as I know. just FYI, our network management cards support changing the port today but also only support basic authentication. on those, SSL/TLS is due at the end of the year in our next major revision.

2.) I would just deal with the agent directly. i believe the SSL certs come up as untrusted because they are created based on the hostname of the computer when you install the software. this there is really no way to get past this besides adding it as a trusted cert or exception. i don't think this is causing the 404. if you can stick with the agent config via web browser, let's do that.

3.) by accessing the agent via web UI, - which means going to the IP address or hostname of the server where its installed on by a.) https://:6547 or b.) http://:3052 - like i said before based on item #2, i think you got here already. when i log in via this method and click on Help on the left hand side navigation bar and go to About, I can see and copy the UPS serial number from here without issue. could you try this?

4.) to configure the silencing of the alarm, click on the UPS name on the left i.e. where it says Smart UPS 1500 or similar, and go to Configuration and you'll see "General Settings" on this page. you'll see Audible alarm and the available configuration options of when you want to hear it.

hope that helps a bit. sorry for the troubles.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 01:15 AM . Last Modified: β€Ž2024-03-11 02:45 AM

0 Likes
0
1668
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 01:15 AM . Last Modified: β€Ž2024-03-11 02:45 AM

Thank you.

I found the serial number and could copy it, quite obvious where to look now that I think about it πŸ˜‰

I did notice the alarm configuration option, and it was set to at power fail, but the UPS still beeped every couple of seconds.
I had to click the navigation button on the UPS front panel, and then the UPS showed silenced, and it stopped beeping.
A silence alarm action button would be more useful than turning the alarm of permanently.

Too bad about the network management card also not supporting SSL/TLS/post config, I already ordered one for unattended notification, that was a fail.

P.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 01:15 AM . Last Modified: β€Ž2024-03-11 02:45 AM

0 Likes
0
1668
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 01:15 AM . Last Modified: β€Ž2024-03-11 02:45 AM

what was the UPS beeping pattern? did you put the UPS on battery to test the beeping or something? i am puzzled as to what settings you are trying to apply and why it is not taking.

NMC2 will at least support the email stuff at the end of the year so its on the horizon.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 01:15 AM . Last Modified: β€Ž2024-03-11 02:45 AM

0 Likes
0
1668
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 01:15 AM . Last Modified: β€Ž2024-03-11 02:45 AM

I installed the NMC2 today, yep, no SSL/TLS/port config for email 😞

Had some trouble finding it on the network, tried the IP detect utility v3 that came on the CD, and the v5 utility I downloaded, neither detected the device. In the end I got the IP from the DHCP server.

I upgraded the firmware to 5.17, and I see the new Schneider branding, and a web option for firmware updates, still requires FTP'in the image, should really be made much simpler to upload images using web interface, vs. requiring me to use a Windows PC to update the firmware.

Looking forward to secure email support, vanilla SMTP is blocked by our FW policy.

P.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 01:16 AM . Last Modified: β€Ž2024-03-11 02:45 AM

0 Likes
0
1669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 01:16 AM . Last Modified: β€Ž2024-03-11 02:45 AM

there are also other firmware upgrade options available that do not require windows, outlined here-> http://nam-en.apc.com/app/answers/detail/a_id/768

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.