AP9630 - The Application Was Not Able to Load

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9630 - The Application Was Not Able to Load
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
VincentDuvernet
Crewman VincentDuvernet
Crewman

Posted: โ€Ž2022-03-29 09:02 AM

0 Likes
11
26168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2022-03-29 09:02 AM

AP9630 - The Application Was Not Able to Load

Hello

 

I'im stuck with the web server message "The Application Was Not Able to Load".

The AP9630 card is inserted into a Smart-UPS 2200 (SRT2200XLI). This AP9630 was inserted into other UPS with the same problem as long as I remember.

 

Prior to this message using firmware 6.9.6 it was a slightliy different message "Application is not compatible with the AOS".

 

I can connect using COM3 or SSH without any problem.

NMC firmware Update Utility don't work:

- FTP "Could not retreive cofiguration configuration file via this method, please recheck settings"

- SCP "Resume not supporter for SCP transfers"

 

I tried without success:

resetToDef โ€“p keepip

format

 

I put files using ftp commands. I was able to upgrade to 7.0.4 but the Stat is still: P+ N4+ N6+ A-

 

Here's the about command :

E000: Success
Hardware Factory
---------------
Model Number: AP9630
Serial Number: ZA1526020265
Hardware Revision: 05
Manufacture Date: 06/22/2015
MAC Address: 00 C0 B7 EB DC 61
Management Uptime: 0 Days 0 Hours 18 Minutes

Application Module
---------------
Name: aos
Version: v7.0.4
Date: Jul 26 2021
Time: 15:26:26

APC OS(AOS)
---------------
Name: aos
Version: v7.0.4
Date: Jul 26 2021
Time: 15:26:26

APC Boot Monitor
---------------
Name: bootmon
Version: v1.0.9
Date: Mar 27 2019
Time: 16:23:06

 

What can I do ?

Thanks,

Vincent

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
brendanmain
Crewman brendanmain
Crewman

Posted: โ€Ž2022-06-24 08:24 PM

In response to VincentDuvernet
0 Likes
4
25663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2022-06-24 08:24 PM

this worked for me 6.6.4 firmware upgrade to new 7.0.4 firmware broke network management card application

 

downgrade to old v5.x firmware using apc firmware update utility 1 which uses FTP, then upgrade to latest firmware using apc firmware update utility 2

 

https://www.se.com/au/en/product/AP9631/ups-network-management-card-2-with-environmental-monitoring/

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
TonKei
Lieutenant TonKei Lieutenant
Lieutenant

Posted: โ€Ž2022-03-29 09:28 AM . Last Modified: โ€Ž2022-03-29 09:29 AM

0 Likes
7
26128
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2022-03-29 09:28 AM . Last Modified: โ€Ž2022-03-29 09:29 AM

Hi Vincent

 

This could look like an issue caused by the application module not being loaded correctly during a firmware upgrade.

My best guess here would be to try doing the upgrade manually, as detailed in the FTP/SCP section of this document:

-> https://www.apc.com/ie/en/faqs/FA156047/

 

You might be able to just skip the bootmon and AOS and jump straight to the APP, but for good measure I would go by the numbers and refresh all 3.

 

Best regards

Tonny

  • Tags:
  • application module
  • english
  • firmware
  • nmc2
Reply

Link copied. Please paste this link to share this article on your social media post.

VincentDuvernet
Crewman VincentDuvernet
Crewman

Posted: โ€Ž2022-03-30 01:38 AM

In response to TonKei
0 Likes
6
26086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2022-03-30 01:38 AM

Hello,

 

This AP9630 card don't have an USB port ๐Ÿ˜ž

I'm unable to access the BootMonitor. I have the green/orange LED blinking quickly but using TeraTerm with 57600/8bits/none/1bit show nothing. Did I do something wrong ?.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

TonKei
Lieutenant TonKei Lieutenant
Lieutenant

Posted: โ€Ž2022-03-30 02:08 AM

In response to VincentDuvernet
0 Likes
0
26075
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2022-03-30 02:08 AM

Hello Vincent

 

The console/serial port on this card is the mini jack port, and to use it, you Will need the console cable that came with the card originally.

 

That being said, I gathered from the information you gave in your previous post, that you have FTP access to the card?

If so, I still suggest following the procedure for using FTP to upgrade the firmware, as detailed in the link from my previous post.

 

Best regards

Tonny

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

brendanmain
Crewman brendanmain
Crewman

Posted: โ€Ž2022-06-24 08:24 PM

In response to VincentDuvernet
0 Likes
4
25664
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2022-06-24 08:24 PM

this worked for me 6.6.4 firmware upgrade to new 7.0.4 firmware broke network management card application

 

downgrade to old v5.x firmware using apc firmware update utility 1 which uses FTP, then upgrade to latest firmware using apc firmware update utility 2

 

https://www.se.com/au/en/product/AP9631/ups-network-management-card-2-with-environmental-monitoring/

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

VincentDuvernet
Crewman VincentDuvernet
Crewman

Posted: โ€Ž2022-08-10 02:25 AM

In response to brendanmain
0 Likes
0
25404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2022-08-10 02:25 AM

Thanks it works ๐Ÿ™‚ it's back to life now

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

cabricharme
Crewman cabricharme
Crewman

Posted: โ€Ž2023-03-21 03:47 PM

In response to brendanmain
0 Likes
1
24024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2023-03-21 03:47 PM

Can't seem to be able to follow this solution - would anyone have a word of wisdom for me?

AP9630 NMC with 5.0.3 firmware on SUA1500RM2U UPS. Attempted to use "Network Management Card v7.0.8 Firmware Executable for Smart-UPS with AP9630/31" to upgrade the firmware, got "unable to update", and then the web UI wouldn't open:

Error: The application was not able to load.
 
You are attempting to access an APC device.

There was a problem loading the application. Please login to the device via telnet for more details.

Can access the CLI (telnet) and FTP.

American Power Conversion               Network Management Card AOS      v5.0.3
(c) Copyright 2009 All Rights Reserved
-------------------------------------------------------------------------------
Name      : **********                                Date : 03/21/2023
Contact   : ******                                    Time : 15:35:14
Location  : **************                            User : Administrator
Up Time   : 0 Days 0 Hours 56 Minutes                 Stat : P+ N+ A-

 

apc>about
E000: Success
Hardware Factory
---------------
Model Number:           AP9630
Serial Number:          ZA102501****
Hardware Revision:      05
Manufacture Date:       06/16/2010
MAC Address:            00 C0 B7 D7 3C A2
Management Uptime:      0 Days 1 Hour 5 Minutes

Application Module
---------------
Name:                   bootmon
Version:                v1.0.9
Date:                   Mar 27 2019
Time:                   16:23:06

APC OS(AOS)
---------------
Name:                   aos
Version:                v5.0.3
Date:                   Aug  4 2009
Time:                   13:12:44

APC Boot Monitor
---------------
Name:                   bootmon
Version:                v1.0.0
Date:                   Oct  8 2008
Time:                   16:03:02
apc>dir
E000: Success
--wx-wx-wx  1 apc      apc      2122752 Aug  4 2009 apc_hw05_aos_503.bin
drwxrwxrwx  1 apc      apc            0 Jan  1 2000 db/
drwxrwxrwx  1 apc      apc            0 Jun 16 2010 ssl/
drwxrwxrwx  1 apc      apc            0 Jun 16 2010 ssh/
drwxrwxrwx  1 apc      apc            0 Jun 16 2010 logs/
drwxrwxrwx  1 apc      apc            0 Jun 16 2010 sec/
drwxrwxrwx  1 apc      apc            0 Jun 16 2010 dbg/
drwxrwxrwx  1 apc      apc            0 Aug 23 2010 scg/

 

It seems that from here I need to manually FTP either the 5.x or 6.x firmware to the NMC and upgrade it that way (still unclear how, exactly). The question is, where do I get 5.x or 6.x firmware? I've tried looking, and all I can see are 7.04 and 7.08 firmware versions.

Thanks!

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

cabricharme
Crewman cabricharme
Crewman

Posted: โ€Ž2023-03-21 03:52 PM . Last Modified: โ€Ž2023-03-21 04:07 PM

In response to cabricharme
0 Likes
0
24022
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2023-03-21 03:52 PM . Last Modified: โ€Ž2023-03-21 04:07 PM

OK, my bad - found it (the firmware): Network Management Card 2 (NMC2) Firmware v6.6.4 Firmware for Smart UPS with AP9630/31/35 and Associ.... Will now try to update it.

... and... that worked! (Didn't even have to FTP into it - the utility did it straight up over the network. The configuration was mostly retained - but did have to redo SNMP strings.)

APC firmware update tool - Screenshot 2023-03-21 160604.png

 

Is it safe to update to 7.08 now?

Reply

Link copied. Please paste this link to share this article on your social media post.

SzS
SzS
Cadet

Posted: โ€Ž2023-11-23 03:11 AM

0 Likes
0
18866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2023-11-23 03:11 AM

Where can I download old v5.x firmware using apc firmware update utility from. The link provided above no longer works. And I have the same problem. After upgrading to 7.1.2 I can not log in.

SzS_0-1700737786218.png

SzS_1-1700737845294.png

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

SzS
SzS
Cadet

Posted: โ€Ž2023-11-23 03:26 AM

In response to brendanmain
0 Likes
0
18968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2023-11-23 03:26 AM

Where can I download old v5.x firmware using apc firmware update utility from. The link provided above no longer works. And I have the same problem. After upgrading to 7.1.2 I can not log in.

SzS_0-1700738768033.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

AG-DE
AG-DE
Cadet

Posted: โ€Ž2023-12-13 05:46 AM

1 Like
1
18537
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2023-12-13 05:46 AM

I had the same error message in browser and also UpdateUtility2 couldn't connect. So I updated 712 aos and sumx bin's as well as 109 bootmon via serial connection (57600 Baud; XMODEM). The problems stood the same. I reconnected via serial port in terminal mode (9600 Baud; user and password 'apc'). After forced password change (requirement in new OS) I did 'about' command. AOS and bootmon were ok but "Application Module --- Invalid Module Header!" Seems there was/is an update problem. Last idea was to connect via FTP. I activated via command "ftp -S enable". UpdateUtility2 still couldn't connect, but WinSCP could. I transferred apc_hw05_sumx_712.bin to the default connected (/root) folder. The file wasn't visible after upload but 'about' showed "Application Module --- Name: sumx Version: v7.1.2". Web interface then worked.

Reply

Link copied. Please paste this link to share this article on your social media post.

kazzic555
kazzic555
Cadet

Posted: โ€Ž2024-01-28 03:27 PM

In response to AG-DE
0 Likes
0
17534
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2024-01-28 03:27 PM

Thank you that fixed my issue also

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore