One of our current 4 UPS's is a LX16000 Tower
Firmware 267.513.I
With an AP9619
Hardware Revision A10
Application Module
sy v3.5.8
APC OS (AOS) aos v3.6.1
Intelligence Modules
Firmware 513 Slave 602
Wanting to use a more updated web interface, I purchased a AP9641
Whilst the card did work in UPS as in I could see the web interface, it could not communicate with the UPS and see the device. Cold restart had same issue.
If I want to use the new card, is there a process or minimum revisions of existing devices to make it happen ??
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-24 08:23 AM
Has the 9641 NMC been flashed with the correct firmware for this specific model UPS? There are several different firmware versions for the Smart-UPS, Symetra, etc.
Lastly, do not install the subscription NMC firmware unless you have a valid subscription! ☝️
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-24 08:23 AM
Has the 9641 NMC been flashed with the correct firmware for this specific model UPS? There are several different firmware versions for the Smart-UPS, Symetra, etc.
Lastly, do not install the subscription NMC firmware unless you have a valid subscription! ☝️
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-28 02:15 PM
Being a new purchase from SE, surely I should be able to load the proper firmware to suit our UPS and 9641 card ?? Without a NMC firmware subscription ??
UPS is a LX16000 3Phase input -> 1Phase output device.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-28 04:36 PM
Thanks Teken. The device was a v3 Card with v2 Firmware so it allowed me to download the v2.5 firmware to suit.
Had it been a v3 firmware, I would need a valid subscription. Although we are considering the sub to get the features that come with v3 mainly the security updates. Although all UPSs are on a locked down vLan