AP8941 unreachable after firmware update

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP8941 unreachable after firmware update
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-27 11:49 PM . Last Modified: ‎2024-03-18 11:50 PM

0 Likes
7
3176
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:49 PM . Last Modified: ‎2024-03-18 11:50 PM

AP8941 unreachable after firmware update

I updated the firmware on two AP8941 units from v5.X.X firmware to the latest 6.4.0 firmware. Both worked fine for several days then one unit became unresponsive with the error "The Application Is Incompatible With This APC OS". This has all the symptoms of "Information Bulletin: Potential Issue with AP8XXXsries Rack Power Distribution Units with rdpu2g v6.0.9 firmware". The LCD is blue with no readout, network port is alternating green/orange, reset button won't reset, even after a hard reset it's still unresponsive. What are my options here, there isn't a newer firmware to update to. I can't down grade the firmware as I need the functionality of the latest firmware, hence the update. I guess I can only reload the current firmware and hope for the best...unless you all have a better suggestion.

Model Number
AP8941
Hardware Revision
02
Manufacture Date
05/19/2012
Rack PDU, APC OS
Version
6.4.0
Boot Monitor
Version
1.0.8

Thanks

 

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • ap8941
  • unreachable
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:49 PM . Last Modified: ‎2024-03-18 11:50 PM

0 Likes
2
3174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:49 PM . Last Modified: ‎2024-03-18 11:50 PM

Hi Justin,

I think I mis-read before. I thought your network port was inactive but I see it said it was alternating green and orange.

If it is a rapid green and orange on the status LED (next to the checkmark and the X), this means the management interface is rebooting. The rapid green and orange is what you get if you press and release the pinhole reset button once. If this is a "slow" green and orange, then it means the PDU is doing a DHCP request.

Did it ever lose its IP at all and you needed to reconfigure?

Can you try reboot command, let it reboot, and then ideally, watch both the display and the status LED I am talking about? I want to know if you see it go through multiple reboot cycles which would be rapid green and orange for like 15 seconds, slow green and orange probably for a few seconds, off, then rapid green and orange again, repeat.

Since we can get to it, we can try to work without the serial cable.

I have a feeling the PDU may be in a reboot loop so after 6 loops, it pauses and you get the A! as you see in your paste of what is on the screen. If you can afford to wipe all the settings from it (maybe you don't have many non-default settings or back up config.ini file), let me know and we can proceed with the format command to wipe ALL settings including TCP/IP network settings. Alternatively, we can try reset to defaults with the keep IP option and see if it clears up any corruption without losing the IP but some junk could linger behind. Not sure, depending on what the issue is.

Let me know if you have any questions before moving forward or on my suggestions.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:49 PM . Last Modified: ‎2024-03-18 11:50 PM

0 Likes
0
3176
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:49 PM . Last Modified: ‎2024-03-18 11:50 PM

Hi Justin,

This just may a coincidence. If you never used v6.0.9 firmware (right, you went from v5->v6.4.0), then there is hope we can recover this. When you get the message about the application being unable to load, it can be because there is a problem with the firmware or that the network management interface tried to boot and couldn't after about 6 times. Sometimes this can be caused by a bad packet on the network or something strange.

Though, because it is COMPLETELY inaccessible, and if you never had 6.0.9 firmware loaded, I am curious. And then you have two units that did it..

We'll need to try the bootmonitor mode/access found in the FAQ about the 6.0.9 firmware as the first and most beneficial step to identifying the problem. This can be tricky timing-wise to access but this does require a local serial connection using the APC serial cable and if the blue display is powering up, the mode should be accessible. Tech support can also guide you through this if you prefer.

Can you clarify the steps you took for "hard reset?" Did that mean power down and back up? If so, did the outlets come back on?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:49 PM . Last Modified: ‎2024-03-18 11:50 PM

0 Likes
0
3176
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:49 PM . Last Modified: ‎2024-03-18 11:50 PM

We updated 2 AP8941 PDUs, one is up and running with no problems the other one....

  • The hard reset was a power down, or should I say we had a building wide power outage.
  • All the outlets are functioning.
  • I'm still able to telnet  into the PDU  and the firmware updater still can communicate with the PDU
  • I tried to reload the firmware and according  to the updater  it was successful however the PDU  is still showing the same error, LCD    screen is still blue
  • I'm not sure we have the serial cable, I came in well after this was setup

[User Name :

[Password  :

Schneider Electric                      Network Management Card AOS      v6.4.0

(c) Copyright 2015 All Rights Reserved  RPDU 2g                          v6.4.0

-------------------------------------------------------------------------------

Name      : PDU02                                     Date : 08/09/2016

Contact   : Unknown                                   Time : 10:06:59

Location  :                            User : Super User

Up Time   : 0 Days 0 Hours 54 Minutes                 Stat : P+ N4+ N6+ A!

Type ? for command listing

Use tcpip command for IP address(-i), subnet(-s), and gateway(-g)

apc>

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:49 PM . Last Modified: ‎2024-03-18 11:50 PM

0 Likes
2
3175
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:49 PM . Last Modified: ‎2024-03-18 11:50 PM

Hi Justin,

I think I mis-read before. I thought your network port was inactive but I see it said it was alternating green and orange.

If it is a rapid green and orange on the status LED (next to the checkmark and the X), this means the management interface is rebooting. The rapid green and orange is what you get if you press and release the pinhole reset button once. If this is a "slow" green and orange, then it means the PDU is doing a DHCP request.

Did it ever lose its IP at all and you needed to reconfigure?

Can you try reboot command, let it reboot, and then ideally, watch both the display and the status LED I am talking about? I want to know if you see it go through multiple reboot cycles which would be rapid green and orange for like 15 seconds, slow green and orange probably for a few seconds, off, then rapid green and orange again, repeat.

Since we can get to it, we can try to work without the serial cable.

I have a feeling the PDU may be in a reboot loop so after 6 loops, it pauses and you get the A! as you see in your paste of what is on the screen. If you can afford to wipe all the settings from it (maybe you don't have many non-default settings or back up config.ini file), let me know and we can proceed with the format command to wipe ALL settings including TCP/IP network settings. Alternatively, we can try reset to defaults with the keep IP option and see if it clears up any corruption without losing the IP but some junk could linger behind. Not sure, depending on what the issue is.

Let me know if you have any questions before moving forward or on my suggestions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-27 11:49 PM . Last Modified: ‎2024-03-18 11:50 PM

0 Likes
0
3176
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:49 PM . Last Modified: ‎2024-03-18 11:50 PM

Hi Angela,

Thank you so much for the info I resetToDef   -p keepip   and the PDU   was back online,   just have some  reconfiguring to do...

Thanks again!!

Justin

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:49 PM . Last Modified: ‎2024-03-18 11:50 PM

0 Likes
0
3176
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:49 PM . Last Modified: ‎2024-03-18 11:50 PM

Hi Justin,

You're welcome. As I am sure you're already thinking, might be a good idea to keep an eye on it to make sure it doesn't happen again because then we have to dig a little deeper perhaps.

Reply

Link copied. Please paste this link to share this article on your social media post.

wegentryjr
wegentryjr
Cadet

Posted: ‎2024-01-26 03:29 PM

In response to BillP
0 Likes
1
2059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-26 03:29 PM

I know this is an old thread, but I have a bunch of 8941's that I need to sanitize. What is the format command you were talking about?

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-01-29 06:18 AM

In response to wegentryjr
0 Likes
0
2037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-29 06:18 AM

Page 47 of the user guide outlines the required steps to complete the format process.

 

I’ve appended a direct link from the APC website here: https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=Switched+Rack+Power...

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore