Posted: 2022-02-07 01:30 PM . Last Modified: 2022-02-07 01:32 PM
Hi,
We attempted to update both our NMC2 cards to the latest firmware. This is what was used:
The NMC2 cards are a AP9630 and AP9630J installed in two Smart UPS 1500VA LCD RM 1Us.
Both updates failed and the NMC2s are now not responsive. I tried doing a hard reset on them holding down the reset button (w/ paper clip) for 20 seconds. Based on the LEDs, the NMC2 cards rebooted but are still unresponsive.
What are my options at this point?
Thank you!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-10 06:37 PM . Last Modified: 2025-05-26 12:11 AM
Thanks for the reply!
That is my next step. I found the following FAQ on how to connect to the serial port and access the bootmonitor:
https://www.se.com/us/en/faqs/FA293874/
However, I am still unclear on what the correct firmware to load is for the AP9630 used in a Smart-UPS 1500 RM 1U.
Can you please provide a link to the correct AP9630 firmware?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-11 12:53 PM
What you have is correct. SUMX stands for Smart-UPS/Matrix. We discontinued the Matrix many years ago but we still provide NMC firmware for those UPS that are still in use.
We do a have a newer version. https://www.apc.com/shop/us/en/products/UPS-Network-Management-Card-v7-0-4-Firmware-for-Smart-UPS-Ga...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-11 06:19 PM
Ok, will give that new version 704 a try over serial. Thanks again for all the help.