Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

AP9630 NM2 card.. safe to remove with UPS on ?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9630 NM2 card.. safe to remove with UPS on ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 02:22 AM . Last Modified: ‎2024-03-05 11:26 PM

0 Likes
7
2158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:22 AM . Last Modified: ‎2024-03-05 11:26 PM

AP9630 NM2 card.. safe to remove with UPS on ?

Hi...

OUR UPS is not showing up in the NM2 when you connect to it via the IP Address.  I want to see if I can get any data on the voltages.

Powerchute console via the Serial port is not working due to the fact that the NM is plugged in... Im trying not to to turn off the UPS as im assuming it will loose any stored data.

Is it ok to remove the NM2 card whilst the UPS Is on ? Im hoping that this will make the Serial port work. I forgot to say we have a SmartUPS 3000

Jason.

heres some recent events from the log

DateTimeEvent
03/26/201315:34:45System: Web user 'apc' logged in from 172.17.19.109.
03/26/201314:46:39UPS: The local network management interface-to-UPS communication not
established.
03/26/201314:45:44System: Network service started. System IP is 172.17.19.48 from manually
configured settings.
03/26/201314:45:28System: Network Interface restarted.
03/26/201313:49:36UPS: The local network management interface-to-UPS communication not
established.
03/26/201313:48:41System: Network service started. System IP is 172.17.19.48 from manually
configured settings.
03/26/201313:48:25System: Network Interface restarted.
03/22/201313:34:19UPS: No longer on battery power.
03/22/201313:34:18UPS: On battery power in response to an input power problem.
03/22/201307:21:35UPS: Passed a self-test.
03/22/201307:21:20UPS: Started a self-test.
03/08/201307:22:54UPS: Passed a self-test.
03/08/201307:22:38UPS: Started a self-test.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • ap9630
  • communication
  • serial
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:22 AM . Last Modified: ‎2024-03-05 11:26 PM

0 Likes
0
2158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:22 AM . Last Modified: ‎2024-03-05 11:26 PM

Yes, most likely. You'll have the data log (which since the card only has so much storage space, you can configure data log rotation and offload it via FTP to an external server for long term storage) and the event log. You might what to consider changing the default logging interval on the data log in particular since the default is every 10 minutes. Depending on your problem, you might need to have it log more frequently. If you do that though, the faster the data gets overwritten (if you do not pursue data log rotation).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:22 AM . Last Modified: ‎2024-03-05 11:26 PM

0 Likes
0
2158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:22 AM . Last Modified: ‎2024-03-05 11:26 PM

Hello - so do you want to try and get the NMC to work? Or do you want to switch to PowerChute?

Yes, you can remove the NMC2 while the UPS is on. Official documented procedure is to "braindead" and turn the UPS off (which basically means to discharge the capacitors) while removing/installing a SmartSlot accessory but there is very little risk and I never do it. I think the risk vs. downtime is not worth it.

Anyway, if you want help getting the AP9630 working, let me know. something has disrupted communication here between the UPS and the management card. We'd want to verify the firmware version (available under Administration->General->About, make sure the serial or USB cables are disconnected, and you could try powercycling the AP9630. You should typically only be using the AP9630 OR powerchute so I am not sure why you'd rather use PowerChute than the management card because its more full powered than PowerChute.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:22 AM . Last Modified: ‎2024-03-05 11:26 PM

0 Likes
0
2158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:22 AM . Last Modified: ‎2024-03-05 11:26 PM

Hi Jason.

I understand the AP9630 NMC is sort of working but not as intended because it cannot communicate with the UPS. While the NMC is in this state, it will not be able to log events or data. The data you see in the management card is stored on the management card and not the UPS so whether or not you turn the UPS off now to get the card working does not matter unfortunately. So, if you cannot see the data from before this issue even now in the management card logs, you won't be able to see it when we get the NMC to start talking to the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 02:22 AM . Last Modified: ‎2024-03-05 11:26 PM

0 Likes
0
2158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:22 AM . Last Modified: ‎2024-03-05 11:26 PM

Hi Angela.

thanks for the reply.

The NMC does work, its just not seeing the UPS at the moment  IT has done in the past.  The NMC is currently repoting "No UPS Found"

We had some sort of power surge on 22/03 at about 13:30 which damaged some not IT related Equipment.  The log on the AP9630 indicates this . Im not sure if there is any useful information I can get from the UPS data that may help us try and put a claim into the Power supplier.  Im not sure if removing thw NMC and connecting the Serial Connection will allow Powerchute to then look at any stored data.

03/22/201313:34:19UPS: No longer on battery power.
03/22/201313:34:18UPS: On battery power in response to an input power problem.

Im sure turning the UPS off and on will make the card see the UPS its actually plugged into. But Im assuming this will mean any stored data I maybe able to get out of the UPS will be lost ?

here is the software data...

Name:sumx
Version:v5.1.6
Date:Aug 11 2011
Time:10:01:53

Name:bootmon
Version:v1.0.2
Date:Jan 21 2010
Time:13:35:57

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 02:22 AM . Last Modified: ‎2024-03-05 11:26 PM

0 Likes
0
2158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:22 AM . Last Modified: ‎2024-03-05 11:26 PM

I would agree with what you are saying but where would powerchute get its data from if you were not using the NMC ?


Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:22 AM . Last Modified: ‎2024-03-05 11:26 PM

0 Likes
0
2158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:22 AM . Last Modified: ‎2024-03-05 11:26 PM

it stores it locally as well as it is gathered (which I am talking about event and data log) - . there are a few items stored on the UPS itself that the NMC or PowerChute displays for you. these items include configuration settings such as self test interval, sensitivity, transfer voltages, etc and it can store a few things like last transfer to battery reason, etc but it is not storing the event log and measure voltages over this time period on the UPS EEPROM itself.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 02:22 AM . Last Modified: ‎2024-03-05 11:26 PM

0 Likes
0
2158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:22 AM . Last Modified: ‎2024-03-05 11:26 PM

Ok so its looks as though I wont be able to get any useful data out of the UPS itself then. For future reference Once I get the Card seeing the UPS proply will it be able to provide any useful data that would assist in a claim to the Electricity Provider ?


Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:22 AM . Last Modified: ‎2024-03-05 11:26 PM

0 Likes
0
2159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:22 AM . Last Modified: ‎2024-03-05 11:26 PM

Yes, most likely. You'll have the data log (which since the card only has so much storage space, you can configure data log rotation and offload it via FTP to an external server for long term storage) and the event log. You might what to consider changing the default logging interval on the data log in particular since the default is every 10 minutes. Depending on your problem, you might need to have it log more frequently. If you do that though, the faster the data gets overwritten (if you do not pursue data log rotation).

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore