AP9619 - stopped emailing alerts

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9619 - stopped emailing alerts
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:30 AM . Last Modified: ‎2024-03-13 05:28 AM

0 Likes
5
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:30 AM . Last Modified: ‎2024-03-13 05:28 AM

AP9619 - stopped emailing alerts

Hello

The following UPS is no longer sending email alerts related to the UPS status, only network card related emails, self-test etc. 

UPS RT 7500 XL 

Hardware factory information   

Model Number:              AP9619

Hardware Revision:        A10

Manufacture Date:        09/13/2005                        

Application module information              

Name: sumx

Version: v2.6.1

Date:    01/14/2005

Time:    11:26:29                          

APC OS(AOS) information          

Name: aos

Version: v2.6.4

Date:    11/12/2004

Time:    19:40:33

Please note I do not have admin rights to my PC and I am administering the system in another country on a global network.

Feedback would be appreciated.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • ap9619
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:30 AM . Last Modified: ‎2024-03-13 05:28 AM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:30 AM . Last Modified: ‎2024-03-13 05:28 AM

On this older AP9619 with 2.X firmware, we don't have a nice export option for the logs on the web. You'd have to copy/paste them into a text file or word document. On 3.X firmware (the latest you can upgrade to), it is a similar situation except it just looks a little nicer when you PDF it and view the log (which can be viewed in a window of its own).

If you want to upgrade it, all of the upgrade methods are available here, one which is FTP which I guess won't work. The Wizard we provide also uses FTP. Refer to NMC1 instructions here. http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156047 

You can get the firmware file from http://www.apc.com/tools/download/index.cfm and Filter by Software/Firmware and select Firmware Upgrades - UPS Network Management Cards and look for SFSUMX372 part number.

I'd suggest copying and pasting what you can before upgrading so we can see what events are being generated in the log and if it's even logging power events to email.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:30 AM . Last Modified: ‎2024-03-13 05:28 AM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:30 AM . Last Modified: ‎2024-03-13 05:28 AM

Dave,

Have you checked the event actions settings on the NMC? There you can configure individual and or groups of events to send or not send e-mails. Click on the Administration tab on the NMC then selects Notification - Event Actions. If you do not have administrative right to the NMC you will need to get them to make changes. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:30 AM . Last Modified: ‎2024-03-13 05:28 AM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:30 AM . Last Modified: ‎2024-03-13 05:28 AM

Reset all the event actions to defaults and added the email address, sent test email which worked, power fails on site no longer trigger an email. The power related events stopped after working for several months.

 I have admin rights to the NMC but not my PC.

  • Tags:
  • ap9619
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:30 AM . Last Modified: ‎2024-03-13 05:28 AM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:30 AM . Last Modified: ‎2024-03-13 05:28 AM

Hello,

I looked at this with Bill. Here are my thoughts/observations/questions:

1.) Your firmware is extremely old on this AP9619. We may consider upgrading after trying a few other options and verifying the current configuration. d

2.) The test email is working so that is good to know. Hopefully this is a configuration issue.

3.) Can you download the config.ini, event.txt, and data.txt files from the AP9619 and attach them here for review? Instructions here (Refer to NMC1) -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156131 

4.) Can you elaborate on the exact text of the event you expect to see for power related events, or give me an example? I'll look to see if they are in the actual logs. We'll make sure they are logged properly and cross check that against the configuration of the events.

Once I look at all of that, then we should know more and see if it makes sense to consider a firmware upgrade or if we've found the problem. Even so, you may want to consider a firmware upgrade to get any bug fixes (even though this product is discontinued as of a years ago anyway).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:30 AM . Last Modified: ‎2024-03-13 05:28 AM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:30 AM . Last Modified: ‎2024-03-13 05:28 AM

Hello, unfortunately FTP access is blocked by the network, and I could not see a way to download the files from the web interface.

What’s the process to update the NMC1 software and will it impact the UPS operation in any way?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:30 AM . Last Modified: ‎2024-03-13 05:28 AM

0 Likes
0
1386
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:30 AM . Last Modified: ‎2024-03-13 05:28 AM

On this older AP9619 with 2.X firmware, we don't have a nice export option for the logs on the web. You'd have to copy/paste them into a text file or word document. On 3.X firmware (the latest you can upgrade to), it is a similar situation except it just looks a little nicer when you PDF it and view the log (which can be viewed in a window of its own).

If you want to upgrade it, all of the upgrade methods are available here, one which is FTP which I guess won't work. The Wizard we provide also uses FTP. Refer to NMC1 instructions here. http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156047 

You can get the firmware file from http://www.apc.com/tools/download/index.cfm and Filter by Software/Firmware and select Firmware Upgrades - UPS Network Management Cards and look for SFSUMX372 part number.

I'd suggest copying and pasting what you can before upgrading so we can see what events are being generated in the log and if it's even logging power events to email.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore