AP9619 cannot reset password

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9619 cannot reset password
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:39 AM

0 Likes
5
3391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:39 AM

AP9619 cannot reset password

I have recently acquired a AP9619 NMC that does not respond to the typical password reset protocol.  I can access the card using "device" username and "apc" password.  However, I cannot log in as administrator as "apc" username seems to have unknown password.  The NMC does not respond to hyperterminal serial access, so I cannot use the reset port on the card to reset to apc/apc log in.  I've tried to upgrade the firmware using ftp with the device/apc login, but it did not work.

Is there an alternate username/password reset procedure that I can try?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-08-19 01:59 PM

In response to BillP
0 Likes
0
3369
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-19 01:59 PM

I changed the password on my AP9619 this morning and now can't log in.  😫  Does it matter which letter is behind the 940-0024 part number?  I see 940-0024 with different letters behind it like C, D, and E.  

 

Thanks  

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:39 AM

0 Likes
0
3386
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:39 AM

Hi Mark,

For this card, you will need serial access. There is no way to reset anything without gaining serial access.

Can you let me know how you connected serially? Do you have an APC serial cable? What were the port settings you used? Or was the issue you don't have the serial cable? Once you had serial access, then you'd need to use the pinhole reset button and press it in the certain manner to allow the administrator credentials to be reset back to apc/apc temporarily as explained here -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156075 

Depending on the specifics of where the trouble is, you'd want to make sure the reset button is intact and actually working as part of the procedure.

Reply

Link copied. Please paste this link to share this article on your social media post.

MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:39 AM

0 Likes
0
3388
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:23 AM . Last Modified: ‎2024-03-13 05:39 AM

I have recently reset similar cards (NMC1's) with the same SU5000 and the proprietary cable at 2400B.  This is the only card that I've had problems with.  The "reset" does cause the LEDs to flash as described.  I think it must be a problem getting the serial interface to work properly.  Is it possible this card needs a different baud setting?   I can get you the aos and sumx file versions if needed?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:39 AM

0 Likes
1
3386
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:39 AM

Hi Mark,

If you suspect it is the serial connection, can you try a different UPS and/or PC to rule those out? And we have a few proprietary cables so I'd just verify it is the 940-0024/1524 cable to make sure maybe you didn't grab the incorrect part number. I also would just double check you don't have SCROLL LOCK stuck on your keyboard as that catches some people once in a while.

You can indeed try different baud rates if someone changed it on you. Here is an article that covers this topic and mentions the valid baud rates -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156126 

At least you know the card itself seems OK if you could pinpoint the issue with the serial connection.

Reply

Link copied. Please paste this link to share this article on your social media post.

MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:39 AM

0 Likes
0
3385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:24 AM . Last Modified: ‎2024-03-13 05:39 AM

Worked at 9600 baud.  Was able to reset password.  FAQ page was helpful also,

Thanks, Mark

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-08-19 01:59 PM

In response to BillP
0 Likes
0
3370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-19 01:59 PM

I changed the password on my AP9619 this morning and now can't log in.  😫  Does it matter which letter is behind the 940-0024 part number?  I see 940-0024 with different letters behind it like C, D, and E.  

 

Thanks  

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore