AP9619 - Default Reset

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9619 - Default Reset
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:34 AM . Last Modified: ‎2024-03-08 02:12 AM

0 Likes
15
16913
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:34 AM . Last Modified: ‎2024-03-08 02:12 AM

AP9619 - Default Reset


Hi,


I have a Smart UPS RT 5000 UPS with a AP9619 Network Management Card. I was have an issue with the network card so I logged onto the web interface and reset the card to default settings. Now I can't find the network card to logon. Before i just ran APC Device IP Configuration Wizard (Remotly over the Network) and it found the card. I know if you push the Reset button it resets the Password but does it reset the TCP/IP settings or there another way to logon (I've tried Telnet).


Thanks

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • management
  • network
  • network_management_card
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

0 Likes
0
16903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

no problem!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 15
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:34 AM . Last Modified: ‎2024-03-08 02:12 AM

0 Likes
0
16902
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:34 AM . Last Modified: ‎2024-03-08 02:12 AM

I have a lead number 940-0144 but not the 940-1525A. I will check in head office tomorrow and try that. The UPS model number is SURTD5000RMXLI.

I can't find any information when searching for that lead thou...

Message was edited by: DThorne

Reply

Link copied. Please paste this link to share this article on your social media post.

EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

0 Likes
0
16904
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

Likely if you've reset it to defaults it's lost it's network settings.

The easiest way to get it back up would be to get local to the UPS and start a terminal session. You'd need the black serial cable (940-0024C should be stamped in the end of it). The terminal settings are 2400,8,none,1, and no flow control.

The default username and password are both "apc". Once logged in you can go to the network properties and get back up and running.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

0 Likes
0
16905
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

Hi,

Thanks for the reply BUT the AP9619 doesn't have a serial port for that lead (See attached Photos of all ports on the UPS). I did a google search and found this: http://www.upsforless.ca/ProductImages/upspics/apc940-0024.jpg is this the lead you mention?

Thanks

david

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

0 Likes
0
16905
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

The card itself doesnt have a serial port on the back of it - the above post refers to the serial port on the UPS. And yes, that is the correct cable. The part number should be stamped on one of the ends of the cable.

But, if you dont see the serial port - double check the model of your UPS - if it is SURTD5000XLT (versus SURT5000XLT), which is a newer UPS, it uses an RJ-45 to Serial cable with a part number of 940-0025 instead of a DB9 to DB9 cable like the 940-0024.

You dont want to hook up any ol cable to this either because there is potential of shutting down the UPS if a non APC cable is used.

Hope this helps!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

0 Likes
0
16905
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

I've upload a few photos of the Smart Card & UPS. I can't seem to find an information on the 940-0025 lead. Is that the correct model?

Thanks again for the help!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

0 Likes
0
16906
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

The cable should have come with the UPS.

Did you confirm the model number on the UPS?

The port labeled "Internal Com" is what you want as you must have the SURTD5000XLT which uses the RJ-45 to DB9 connector. I confirmed the actual part number is a 15 foot cable that is shipping with this model - 940-1525A is the exact part number I dug up.

I attached the manual - check page 4 in the manual, page 6 of the actual PDF file. It shows a picture on the page I mentioned of the connector in the picture.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

0 Likes
0
16906
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

940-0144 is used to configure APC's rackmount PDUs.

The SURTD models are very new so that must be why the cables arent out there as much as the 940-0024 cables as you can see online.

I am 110% sure that is the correct cable though. At least it will narrow it down from other serial cables since its RJ-45 to serial.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

0 Likes
0
16906
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

I've can't find that lead at HQ but I've spoken to the supplier who I ordered the UPS from and getting a new lead. This will take a few days then I will try again and let you know.

Thanks for all your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

0 Likes
0
16904
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

no problem!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

0 Likes
0
16906
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

Thanks all!!

Got the lead today and configured the UPS!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

0 Likes
0
16906
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

good to hear.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

0 Likes
0
16906
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

We have a Symetra PX 40kVa with an ap9617 installed. after resetting the password to a different one than default we can't access it neither thru serial or web interface. We have tried the procedure described on the manual for password recovery but it doesn't works .

Any ideas on how to bring it to factory defaults? Are we doomed?

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

0 Likes
0
16906
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

I've never seen the password recovery fail.

When you're doing it, there's a little asterisk that should be placed in the notes.

After pressing the reset button a first time, the lights will alternately flash.
Press it again, they'll go out.

As soon as they go out, make sure you already have Hyperterminal open, and start pounding enter.

As soon as you get a User Name prompt, enter the "apc" for username and "apc" for password

It times out after 15 seconds, so that is normally where the failure lies.

Most customers aren't aware of that quick timeout, therefore it fails each time.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

0 Likes
0
16906
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:12 AM

Where can I buy a 940-0025 Serial cable?.  I have a AP9619 with the cat 5 connection only. Thank you!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:11 AM

0 Likes
0
16906
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:35 AM . Last Modified: ‎2024-03-08 02:11 AM

Hi,

Smart-UPS with model numbers SU and SUA use the 940-0024 serial cable. Smart-UPS with model numbers SMT, SMX, SMC, SRT, SURTD use the 940-0625 serial cable. Both cable are available on apc.com and others site like CDW, and Amazon.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.