AP9617 missing Apparent Load Power & Load Current after upgrade

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9617 missing Apparent Load Power & Load Current after upgrade
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:32 AM . Last Modified: ‎2024-03-18 12:23 AM

0 Likes
6
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:32 AM . Last Modified: ‎2024-03-18 12:23 AM

AP9617 missing Apparent Load Power & Load Current after upgrade

I have 2 Smart-UPS 1500 RM, each with an AP9617 management card in them.

Prior to upgrading both UPS to apc_hw02_aos_373.bin (apc_hw02_sumx_372.bin), I was able to view the current load in amps via the web interface or via snmp (oid .1.3.6.1.4.1.318.1.1.1.4.2.4.0).

I upgraded both units at the same time and using the same firmware files.

Now 1 unit will show the current load and 1 will not. 

Working
Model: Smart-UPS 1500 RM
Serial Number: WQ0807160068
Firmware Revision: 667.18.D
Manufacture Date: 07/21/09

Not Working
Model: Smart-UPS 1500 RM
Serial Number: AS0548235287
Firmware Revision: 617.3.D
Manufacture Date: 11/27/05
I know these are old UPS's and old management cards, but I am really curious why both displayed the current load in amps via snmp prior but not after.
I can provide snmpwalk output for both Units if needed, but the oid is totally missing from AS0548235287
Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:32 AM . Last Modified: ‎2024-03-18 12:23 AM

0 Likes
0
1996
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:32 AM . Last Modified: ‎2024-03-18 12:23 AM

Yes, I keep both APC's fairly balanced so it reported within 1amp of the other unit, which made sense.

That oid doesn't exist when I snmpwalk that unit, so I guess that part was removed from the code for that model, but I am interested to see if it was intentional or the reason why.

Thanks again!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:32 AM . Last Modified: ‎2024-03-18 12:23 AM

0 Likes
0
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:32 AM . Last Modified: ‎2024-03-18 12:23 AM

Hello,

Which version did you upgrade from?

I believe we did intentionally make changes in this area back in the day due to the fact that some UPSs shouldn't have been reporting certain values to begin with based on what they truly support in their own firmware.

Before we begin, I know that you showed us through NMC, these both report as Smart-UPS 1500 - can you confirm what their exact SKU is from the sticker on the actual UPS itself? Something like SUA1500 or SURT1500? That way, I can verify what I am thinking is happening is true where we made those changes I mentioned and I can clearly explain it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:32 AM . Last Modified: ‎2024-03-18 12:23 AM

0 Likes
0
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:32 AM . Last Modified: ‎2024-03-18 12:23 AM

The OS version was very old (AOS 2.1?), I think it was dated 2003

Works
SUA1500R2X122
WQ0807160068

Not Working
SUA1500RM2U
AS0548235287

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:32 AM . Last Modified: ‎2024-03-18 12:23 AM

0 Likes
0
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:32 AM . Last Modified: ‎2024-03-18 12:23 AM

Hi John,

Sorry for the delay. I was asking a few colleagues to help try and figure out what is going on.

My first question is - were you seeing 0 for output current or was it actually showing data properly?

The reality is that the two UPSs you have, even though they are similar model numbers, are different generations internally and specific to the firmware platform. The SUA1500R2X122 is a "4G" from 2008 and the SUA1500RM2U from 2005 (year of mfg seen in serial numbers), based on its firmware is what we call a 3.6G meaning it was developed between the 3rd and 4th generation models that are historically designated by their SU and SUA prefixes and the model number. Yours have both SUA of course.

The UPS team confirmed they only added support for output current and VA (apparent load) in 4G units unfortunately.

Now, back to my original thought I was getting at and with the above considered, I think the NMC firmware did a "clean up" at some point where it stopped showing 0 or other erroneous values when it should be N/A because the UPS does not support it to begin with. 

Let me know if you have any questions or feedback on this. We could always get you a firmware downgrade if you wanted it (wouldn't recommend that) but then it is likely the values you were seeing before were erroneous in some way.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:32 AM . Last Modified: ‎2024-03-18 12:23 AM

0 Likes
0
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:32 AM . Last Modified: ‎2024-03-18 12:23 AM

Oddly enough it used to show output current of 1 or 2amps. I do appreciate you checking this out. It's not a huge deal, I just disabled that field in my monitoring system. I guess losing that oid is a small price to pay for a more modern firmware.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:32 AM . Last Modified: ‎2024-03-18 12:23 AM

0 Likes
0
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:32 AM . Last Modified: ‎2024-03-18 12:23 AM

Hmm, and the 1 or 2 amps for load must have made sense, right? Meaning you have a small load on the UPS and didn't expect to see something like 10 or 12? It's piqued my interest as it did yours so was just asking. Understood you'll stop checking on it with your monitoring tool.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:32 AM . Last Modified: ‎2024-03-18 12:23 AM

0 Likes
0
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:32 AM . Last Modified: ‎2024-03-18 12:23 AM

Yes, I keep both APC's fairly balanced so it reported within 1amp of the other unit, which made sense.

That oid doesn't exist when I snmpwalk that unit, so I guess that part was removed from the code for that model, but I am interested to see if it was intentional or the reason why.

Thanks again!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore