Alert UPS: Bypass not in range ; either frequency or voltage.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Alert UPS: Bypass not in range ; either frequency or voltage.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:31 AM . Last Modified: ‎2024-03-18 12:23 AM

0 Likes
1
3109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:31 AM . Last Modified: ‎2024-03-18 12:23 AM

Alert UPS: Bypass not in range ; either frequency or voltage.

Hi, 

We are noticing a number of events on our UPS so often. We have 3 Smart SRT 6000 in our server room and all three were generating alerts every couple of months. 

  02/24/2018 07:35:54 UPS: No longer on battery power.
  02/24/2018 07:35:53 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.
  02/24/2018 07:35:53 UPS: On battery power in response to rapid change of input.
  02/24/2018 07:35:53 UPS: Bypass not in range ; either frequency or voltage.
  02/24/2018 06:46:35 UPS: No longer on battery power.

We have complained to building management and they confirmed that there are no issues with their equipment or they have noticed any input fluctuation during that peirod. Also, other tenants have no complaints about any such fluctuation same time. 

I did log a support ticket with APC but have not got any satisfactory answer on it. 

Did anyone have any clue what's going on?

Thanks,

Vaibhav 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:31 AM . Last Modified: ‎2024-03-18 12:23 AM

0 Likes
0
3103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:31 AM . Last Modified: ‎2024-03-18 12:23 AM

Hi Vaibhav - 

This is a safety measure which keeps the UPS from switching to bybass if the input power is outside of a set parameter. If you could provide the data log from the time frame that you see the errors, we can probably give you a better answer of what exactly why this is happening. If you want to change your bypass limites you can do that via the web interface of the UPS. Go to "Configuration" then "Power Settings". You will see options for Bypass upper and lower voltages. You can set them to whatever you are comfortable with for the equipment you have attached.

One other note - These messages are much more common if you have the output voltage set to a different voltage than your nominal input voltage. For example - An SRT6KRMXLT is a nominal 208v unit. If you are feeding it 240v it will still output 208v unless you manually set it to output 240v via the Configuration/Power settings menu. For best performance your output should match the input voltage.  One note - If you need to change the output voltage of the UPS the output must be turned OFF when you make the change. The UPS will not allow you to change output voltages live.

Thanks!

Liam

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:31 AM . Last Modified: ‎2024-03-18 12:23 AM

0 Likes
0
3104
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:31 AM . Last Modified: ‎2024-03-18 12:23 AM

Hi Vaibhav - 

This is a safety measure which keeps the UPS from switching to bybass if the input power is outside of a set parameter. If you could provide the data log from the time frame that you see the errors, we can probably give you a better answer of what exactly why this is happening. If you want to change your bypass limites you can do that via the web interface of the UPS. Go to "Configuration" then "Power Settings". You will see options for Bypass upper and lower voltages. You can set them to whatever you are comfortable with for the equipment you have attached.

One other note - These messages are much more common if you have the output voltage set to a different voltage than your nominal input voltage. For example - An SRT6KRMXLT is a nominal 208v unit. If you are feeding it 240v it will still output 208v unless you manually set it to output 240v via the Configuration/Power settings menu. For best performance your output should match the input voltage.  One note - If you need to change the output voltage of the UPS the output must be turned OFF when you make the change. The UPS will not allow you to change output voltages live.

Thanks!

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now