AP9617 & SU1400NET

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9617 & SU1400NET
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:21 AM . Last Modified: ‎2024-03-06 01:50 AM

0 Likes
3
1448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:21 AM . Last Modified: ‎2024-03-06 01:50 AM

AP9617 & SU1400NET

So, I got a 'new' UPS the other day.

Considering the old UPS was a SmartUPS-1250, its 'new' to me. Namely, there's a smartslot in it. So, having put the datacenter Symmetra and Silcons online, I wanted to put my UPS on. I'm pretty sure I used AP9617s or AP9618s depending on location.

Anyways...I found an extra AP9617, but can't seem to get it to upgrade.

Its doing this:

American Power Conversion Network Management Card AOS v2.1.0
(c) Copyright 2002 All Rights Reserved
-------------------------------------------------------------------------------
Name : Unknown Date : 06/23/2012
Contact : Unknown Time : 22:20:32
Location : Unknown User : Administrator
Up Time : 0 Days 0 Hours 9 Minutes Stat : P+ N+ A-


------- Control Console -------------------------------------------------------

About System

Model Number : AP9617
Serial Number : JAxxxxxxxxxx
Manufacture Date : 09/25/2003
Hardware Revision : A10
MAC Address : 00 C0 B7 6B 03 A8
Flash Type : AMD A29DL322DB

Press to continue...

-----------------------------------------------------------------------
Module Information

Description : Network Management Card AOS
-----------------------------------------------------------------------
Name : aos Type : APC OS
Version : 373 Sector : 12
Date : 02/02/2010 Time : 17:05:14
CRC16 : B630

Press to continue...

Description : Network Management Card AOS
-----------------------------------------------------------------------
Name : aos Type : APC OS
Version : 210 Sector : 51
Date : 06/04/2003 Time : 16:22:58
CRC16 : DA3B

Press to continue...

Message was edited by: lkchen

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:21 AM . Last Modified: ‎2024-03-06 01:50 AM

0 Likes
0
1447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:21 AM . Last Modified: ‎2024-03-06 01:50 AM

what do you mean specifically by it does not work? your firmware looks good so if the AP9617 is not communicating with the UPS, I would make sure we "braindead" the UPS to reset/reboot it. To do this, you need to turn off and remove all load from the UPS and turn off the UPS as well. then unplug it from the wall/remove AC power and hold down the off (o) button on the UPS and see if you hear an audible click and/or see the LEDs flash on the UPS. if this does not happen, leave the UPS alone for about 10 minutes and this condition will occur on its own. make sure to disconnect any serial cables during this procedure too.

turn it back on and see if the network management card (without serial able connected) is communicating with the UPS.

if you mean something else isnt working, let me know.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
clahote_apc
Crewman clahote_apc
Crewman

Posted: ‎2021-07-01 01:21 AM . Last Modified: ‎2024-03-06 01:50 AM

0 Likes
0
1447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:21 AM . Last Modified: ‎2024-03-06 01:50 AM

The A- and A! status flags are an indication that the card is not communicating with the UPS.

A- = Bad checksum
A! = Wrong APP for AOS

http://nam-en.apc.com/app/answers/detail/a_id/9318/~/what-does-the-p-n-a-mean-on-stat-section-of-my-...

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:21 AM . Last Modified: ‎2024-03-06 01:50 AM

0 Likes
0
1447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:21 AM . Last Modified: ‎2024-03-06 01:50 AM

So after lots of trial and error....I eventually got the AOS updated.

Had to do it over serial at 2400 bps. Wouldn't work FTP to the card, FTP from the card or using TFTP...or serial at faster speeds.

And, then also had to do sumx using serial at 2400 bps.

But, still doesn't work.

American Power Conversion Network Management Card AOS v3.7.3
(c) Copyright 2009 All Rights Reserved Smart-UPS & Matrix-UPS APP v3.7.2
-------------------------------------------------------------------------------
Name : Unknown Date : 07/21/2012
Contact : Unknown Time : 22:42:21
Location : Unknown User : Administrator
Up Time : 0 Days 0 Hours 0 Minutes Stat : P+ N+ A!


------- Control Console -------------------------------------------------------


-----------------------------------------------------------------------
About System

Model Number : AP9617
Serial Number : JA0339031186
Manufacture Date : 09/25/2003
Hardware Revision : A10
MAC Address : 00 C0 B7 6B 03 A8
Flash Type : AMD A29DL322DB

Press to continue...

-----------------------------------------------------------------------
Module Information

Description : Smart-UPS & Matrix-UPS APP
-----------------------------------------------------------------------
Name : sumx Type : StatApp
Version : 372 Sector : 16
Date : 02/02/2010 Time : 19:08:16
CRC16 : EFCA

Press to continue...

Description : Network Management Card AOS
-----------------------------------------------------------------------
Name : aos Type : APC OS
Version : 373 Sector : 47
Date : 02/02/2010 Time : 17:05:14
CRC16 : B630

Press to continue...

Message was edited by: lkchen

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:21 AM . Last Modified: ‎2024-03-06 01:50 AM

0 Likes
0
1448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:21 AM . Last Modified: ‎2024-03-06 01:50 AM

what do you mean specifically by it does not work? your firmware looks good so if the AP9617 is not communicating with the UPS, I would make sure we "braindead" the UPS to reset/reboot it. To do this, you need to turn off and remove all load from the UPS and turn off the UPS as well. then unplug it from the wall/remove AC power and hold down the off (o) button on the UPS and see if you hear an audible click and/or see the LEDs flash on the UPS. if this does not happen, leave the UPS alone for about 10 minutes and this condition will occur on its own. make sure to disconnect any serial cables during this procedure too.

turn it back on and see if the network management card (without serial able connected) is communicating with the UPS.

if you mean something else isnt working, let me know.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore