AIX PCNS shutdown sequence issue.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AIX PCNS shutdown sequence issue.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:21 AM . Last Modified: ‎2024-03-06 01:51 AM

0 Likes
2
651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:21 AM . Last Modified: ‎2024-03-06 01:51 AM

AIX PCNS shutdown sequence issue.

I have a few AIX virtual sitting on one AIX host. I have installed PCNS AIX v2.2.4 and setup that the VM shutdown first before the host.
The VM is set to shutdown after 5 mins on battery. The host is 10mins after on battery. I have installed PCNS AIX for both host and virtual.
But when shutdown command is issued, the VM and the host are triggered to shutdown at the same time. Not in sequence as I have configured.
Is there any additional settings that need to be configured on the PCNS or the host or this is a bug?
Thanks.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:21 AM . Last Modified: ‎2024-03-06 01:51 AM

0 Likes
0
651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:21 AM . Last Modified: ‎2024-03-06 01:51 AM

Hi Viostar,

Thanks for your input. But I remember that each PCNS does not have "Turn off UPS after shutdown finishes" checked.
I am not sure you are referring to this option in your reply earlier.
Anyway, I found that the hosts actually start to shutdown 1 second later than all the VMs.
During that time the VM's are still shutting down, so not sure if the option is the culprit.
Thanks.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 01:21 AM . Last Modified: ‎2024-03-06 01:51 AM

0 Likes
0
651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:21 AM . Last Modified: ‎2024-03-06 01:51 AM

My guess is the VM is set to shutdown the UPS (it's a checkbox in the PCNS GUI). That, in turn, causes the host to shutdown.

Some options:
- Have only the host shutdown the UPS. That means if power comes back before the host starts a UPS shutdown, you'll need to manually start the VM (assuming the VM will start when the host starts up).
- Have the host and VM trigger at the same time, but use the "script execution delay" to delay the host shutdown. This is probably what you want.
- Have only the host run PCNS and use the command script to shutdown the VM or perhaps the VM management software will automatically do this.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:21 AM . Last Modified: ‎2024-03-06 01:51 AM

0 Likes
0
652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:21 AM . Last Modified: ‎2024-03-06 01:51 AM

Hi Viostar,

Thanks for your input. But I remember that each PCNS does not have "Turn off UPS after shutdown finishes" checked.
I am not sure you are referring to this option in your reply earlier.
Anyway, I found that the hosts actually start to shutdown 1 second later than all the VMs.
During that time the VM's are still shutting down, so not sure if the option is the culprit.
Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login