We have a Symmetra PX 20k with an AP9617 mgmt card. Firmware was apc_hw02_aos_264.bin prior to upgrade
Went to this page and selected the 3.7.2 firmware:
http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=ISX20K20F&total_watts=20000...
Ran the install, and it said that it had failed. Here are the contents of the result.txt file:
________________________________________________________________________
Using AOS file : AOS = apc_hw02_aos_373.bin
Using Application file: APP = apc_hw02_sy3p_372.bin
Checking network connection ... Checking version information ...
*************** Next **************
Before Upgrading the NMC the AOS is: apc_hw02_aos_264.bin
Attempting to log in to x.x.x.x ... Log in sucessful
Loading OS, please wait ... OK
Please wait (2 minutes ) for system restart OK
Attempting connection to verify restart Failed to ping at x.x.x.xSystem reboot failed. Aborting this Upgrade.
Not all Network Management Cards were upgraded successfully:
x.x.x.x: The Management Card at this address is not responsive.
Encountered 1 failures during upgrade.
____________________________________________________________________________________
I can still ping the IP and I can login through telnet, but I cannot access the web interface. The error that comes up is:
Error: The application was not able to load.
You are attempting to access an APC device.
There was a problem loading the application. Please login to the device via telnet for more details.
Message was edited by: joerockt
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 01:16 AM . Last Modified: 2024-03-06 01:55 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 01:16 AM . Last Modified: 2024-03-06 01:55 AM
That did it. Thank you very much.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 01:16 AM . Last Modified: 2024-03-06 01:55 AM
hello,
follow the manual FTP instructions for NMC1 (AP9617/18/19) in this article below and it should resolve the issue:
http://nam-en.apc.com/app/answers/detail/a_id/768
you'll need the .bin firmware files from the download you got off the website.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 01:16 AM . Last Modified: 2024-03-06 01:55 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 01:16 AM . Last Modified: 2024-03-06 01:55 AM
That did it. Thank you very much.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.